[RE-wrenches] Different LFP Batteries in Parallel
Steve Higgins
steve at surrette.com
Mon Jul 14 09:46:05 EDT 2025
I wouldn't do it... By doing so, you'll likely void any manufacturer's
warranty.
If you must do it, I would manually balance the old/new banks every 60-90
days. This involves separating the parallel strings of batteries and
charging each string independently to achieve a full charge. If you don't
do this, the different ages can cause imbalances, which will lead to
problems with the BMS, regardless of whether it is in open-loop or
closed-loop configuration.
*Steve Higgins* *⋅* *Technical Services Manager*
*t* +1.902.597.4020 *m* +1.206.790.5840
*f* +1.902.597.8447 *e* steve at surrette.com
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------
On Mon, Jul 14, 2025 at 4:09 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> There are never-ending videos on YouTube showing different brands and
> capacities of LFP batteries working in parallel. I have never tried it
> myself, and every instinct says don't do it, but I have a situation where
> it would be very helpful.
>
> I have a client with an older 60 kWh battery that is discontinued and
> incompatible with any other battery from the same manufacturer. It has a
> BMS with a 51.2 volt nominal rating. They need another 20 kWh of capacity.
> It is too costly to scrap the existing battery and start over, and the
> existing battery has been tested and confirmed to hold very close to its
> rated capacity.
>
> What is the real deal on mixing and matching? Is anyone doing this safely
> and successfully? I wonder what the battery manufacturers say about it.
>
> Jason Szumlanski
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250714/bd092fb9/attachment.htm>
More information about the RE-Wrenches
mailing list