[RE-wrenches] Backing up a 400A main with two 200-amp main panels: separate or combine with more complexity and use external ATS?
Jerry Shafer
jerrysgarage01 at gmail.com
Sun Jun 29 13:26:49 EDT 2025
Wrenches, Howard,
So first issue I see with the ATS is it will not disconnect the grid if the
EC aka Gen set input has no power. I am currently installing a system on a
800/1000 amp, in the past they had ASCO 200 a ATS's installed l am backing
up 3 of the 5 with solark 15 and 3 fortress batteries, the customer doesn't
want to waist the time doing load verifications, the inverters are
replacing the ATS's and will now command the genset, in the future we may
need an additional inverter. Don't over think it then over engineer it,
complexity leads to complications
On Sun, Jun 29, 2025, 8:04 AM Chris Sparadeo via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi Scot,
>
> In my experience backing up a 400A service with two Sol-Ark 15K inverters,
> it's critical to use a single battery bank and to parallel both the
> inverter inputs and outputs. I initially attempted to configure two
> interdependent Sol-Arks to work together, but encountered monitoring
> communication issues and was informed by Sol-Ark tech support that data
> would be skewed if the inverteres were on the same utility transformer and
> were not run in parallel. Hope this helps.
>
> Best,
>
> Chris
>
> On Fri, Jun 27, 2025 at 3:05 PM scot.arey--- via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Seeking your feedback and best practices.
>>
>>
>> We have a existing customer who wants to add ESS for whole house backup.
>> He has a 400-amp meter box with two 200-amp panels on each side of the
>> meter can. We want to use Sol-Ark and HomeGrid which is our go-to solution.
>> Today, we have two 10KW ground mounts feeding a grid-tied system with
>> Fronius inverters aggregated at the array with single set of conductors
>> back to the house and meter
>>
>> Option 1: Add a SolArk 15KW and HomeGrid '4-stack' per each 200-amp
>> panel and in essence have two separate systems each backing up their own
>> panelboard. Seems easy but I know the panels are not totally balanced and
>> this seems like I'm having excess capacity at the panel that powers
>> circuits to run less than all the time.
>>
>> Brings me to option 2:
>>
>> Install two paralleled SolArks with two batteries again (and now a
>> battery combiner) and add a 400-amp transfer switch and take grid output
>> from meter and bring to ATS first. The GEN inputs on ATS will be fed by
>> aggregated LOAD outputs of the SolArks so if grid fails, the ATS "sees"
>> 240V and transfers to the inverters only and opens circuit to grid. When
>> grid power is there, all is grid-tied and bi-directional. I've done similar
>> setup with Outback Radian and ASCO 200A ATS for whole house backup.
>>
>> But this seems really complicated with lots of extra boxes.
>>
>> Take the simple-easy route even if one inverter is a bit too much for one
>> of the 200-amp panels? Ot aggregate and use ATS so we can put two SolArks
>> to work together to address full load as one operating output? Wall space
>> for this is pretty good for both options.
>>
>> *Howard "Scot" Arey*
>> *Owner, Solar CenTex*
>>
>> NABCEP PV Installation Professional
>> TECL 29755
>> 254-300-1228
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250629/402c6bec/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-4krqxd1o.png
Type: image/png
Size: 294949 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250629/402c6bec/attachment.png>
More information about the RE-Wrenches
mailing list