[RE-wrenches] Backing up a 400A main with two 200-amp main panels: separate or combine with more complexity and use external ATS?

scot.arey at solarcentex.com scot.arey at solarcentex.com
Fri Jun 27 15:05:09 EDT 2025


Seeking your feedback and best practices.


We have a existing customer who wants to add ESS for whole house backup. He has a 400-amp meter box with two 200-amp panels on each side of the meter can. We want to use Sol-Ark and HomeGrid which is our go-to solution. Today, we have two 10KW ground mounts feeding a grid-tied system with Fronius inverters aggregated at the array with single set of conductors back to the house and meter

Option 1: Add a SolArk 15KW and HomeGrid '4-stack' per each 200-amp panel and in essence have two separate systems each backing up their own panelboard. Seems easy but I know the panels are not totally balanced and this seems like I'm having excess capacity at the panel that powers circuits to run less than all the time.

Brings me to option 2:

Install two paralleled SolArks with two batteries again (and now a battery combiner) and add a 400-amp transfer switch and take grid output from meter and bring to ATS first. The GEN inputs on ATS will be fed by aggregated LOAD outputs of the SolArks so if grid fails, the ATS "sees" 240V and transfers to the inverters only  and opens circuit to grid. When grid power is there, all is grid-tied and bi-directional. I've done similar setup with Outback Radian and ASCO 200A ATS for whole house backup.

But this seems really complicated with lots of extra boxes.

Take the simple-easy route even if one inverter is a bit too much for one of the 200-amp panels? Ot aggregate and use ATS so we can put two SolArks to work together to address full load as one operating output? Wall space for this is pretty good for both options.

Howard "Scot" Arey
Owner, Solar CenTex

NABCEP PV Installation Professional
TECL 29755
254-300-1228
[cid:93072a27-74f6-4f45-9077-8804c1dd86e5]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250627/6a8c0fb5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-4krqxd1o.png
Type: image/png
Size: 294949 bytes
Desc: Outlook-4krqxd1o.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250627/6a8c0fb5/attachment.png>


More information about the RE-Wrenches mailing list