You are referring to a distinction between “PV Source” versus “PV Output”
circuits. Unfortunately, according to the code all “PV system circuits”
are considered when determining the requirement for RSS. As I see it, the
disconnect you suggest does not remove the requirement for RSS if any “PV
System circuit” is “installed on or in” a structure that is intended for
any use in addition to housing PV equipment. This applies to a ground-mount
PV array.
I am not arguing the requirement makes sense—I believe it does not. I am
just suggesting how a literal reading of the code would be interpreted.
Being able to understand this will prepare us to anticipate what a building
inspector or plan checker might require.
See text of code below.
*690.12 Rapid Shutdown of PV Systems on Buildings. **PV*
*system circuits installed on or in buildings shall include a rapid*
*shutdown function to reduce shock hazard for firefighters in*
*accordance with 690.12(A) through (D).*
*Exception: Ground-mounted PV system circuits that enter buildings,*
*of which the sole purpose is to house PV system equipment,*
*shall not be required to comply with 690.12.*
I would argue that if you could mount the outdoor portion of the mini-split
on a backboard or pad separated even inches from the home, you would not be
required to have RSS.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Ray Walters via RE-wrenches
*Sent:* Thursday, June 19, 2025 8:34 AM
*To:* re-wrenches at lists.re-wrenches.org
*Cc:* Ray Walters
*Subject:* Re: [RE-wrenches] EG4 Mini Split
The PV circuit stops at the PV disconnect. Put the PV disconnect on the
wall before it comes in, then RSS is NOT required.