[RE-wrenches] 500V "Crowbar"

david quattro david at quattrosolar.com
Mon Jun 16 17:07:09 EDT 2025


Travis, sounds like you are not able to re-string the array to conform to
500V max?

On Mon, Jun 16, 2025 at 1:42 PM Travis Knipple via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hi all,
>
> This is a repeated (rephrased) version of a previous question, but I've
> hit upon a new application.
> I'm looking to retrofit a system from existing SMA Sunny Boy inverters to
> work with an ESS System.
> My PV Array (~900' from the inverters) is 600V Voc, and the strings are
> combined at the Array, so Imp is 24A, Isc is 32A.
> Also, important to note is that 1 of my SB7000 inverters is non functional.
>
> So, my options are:
> (A) A 500V "Crowbar" or SRC type circuit to limit my Voc, and allow me to
> take the array directly to a single MPPT port on a Sol-ark Inverter
> Or, use AC-Coupling to the Sol-Ark, then I can...
> (B) A new PV Inverter that can handle 600V, 32A (Isc) on a single MPPT Port
> (C) A replacement SB7000
> (D) Re-pull my strings of wires to something like a Solis PV Inverter
>
> Does anyone know of either:
> (A) a Voc limiter?
> (B) A PV Inverter with a single MPPT input that can handle 600V, 24A
> (Imp), 32A (Isc)
> or
> (C) A source for a replacement SB7000US
>
> --
> Travis Knipple
> Senior Engineer
> Hudson Solar Solutions LLC
> Rhinebeck, NY 12572
> 518-539-8040 x408 | travis at hudsonsolarsolutions.com
>
> PVIP# PV-111821-013612
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>