[RE-wrenches] Fire Rating for Battery Room
Nicholas Ponzio
nponzio at buildingenergyus.com
Fri Jun 6 09:17:01 EDT 2025
For those of you installing batteries inside homes how are you treating
this poorly-worded section of Code?
*NFPA 855 - 15.4.2:*
*If the room or space where the ESS is to be installed is not finished or
non-combustible, the walls and ceilings of the room or space shall be
protected with not less than 5/8 in. Type X gypsum board.*
This section of fire code has given us much consternation over the years.
Most installations in this climate are going into unfinished basements. Are
you all installing 5/8 sheetrock for the entire basement? Just the area
around the batteries? Something else?
Thanks in advance for any thoughts.
--
Nicholas Ponzio
Building Energy
1570 South Brownell Road
Williston, VT 05495
http://www.BuildingEnergyVT.com <http://www.buildingenergyvt.com/>
"Building Solutions for a Sustainable Future"
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250606/19361c93/attachment.htm>
More information about the RE-Wrenches
mailing list