Hi Scott,

Attached is the datasheet for the AP smart transmitter. It has data on
maximum current, modules, and number of strings.

However, I have a follow up question. This datasheet also says that the
coil is 12V, 800mA. But the Sol-Ark manual specifies 12V, 100mA. Has anyone
had issues with the Sol-Ark not being able to properly power the coil?

Cheers,
Dave

On Thu, Jun 5, 2025 at 3:03 PM scot.arey--- via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Before this, never had need to install RSD with Sol-Ark but doing project
> now that does. SolArk manual very clear on the pins to use but the APSmart
> manual leaves some open questions.
>
> Question is: How many strings of PV Modules can I route through single
> coil?
>
> Here we have four strings of 9-modules so I'm well below max string length
> of 30. But the manual is silent on number of strings through a coil. There
> is max amperage rating thru the coil (which looks like CT) but is it just
> one string per coil? Hope not. Each APSmart transmitter can handle two
> coils. Here is pic for reference from the SolArk manual.
>
>
> *Howard "Scot" Arey*
> *Owner, Solar CenTex*
>
> NABCEP PV Installation Professional
> TECL 29755
> 254-300-1228
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250605/69f664ca/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 679754 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250605/69f664ca/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-xkjfzqf2.png
Type: image/png
Size: 294949 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250605/69f664ca/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 4301515202_Transmitter-PLC-datasheet_Rev2.4_2022-06-20.pdf
Type: application/pdf
Size: 362960 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250605/69f664ca/attachment.pdf>


More information about the RE-Wrenches mailing list