Screens were from cloud but should be similar on SCP. Device
numbers must be different!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2025-05-31 9:56 am, Dave Angelini Offgrid Solar wrote:
> Monday thru Friday. They may tell you that XW+ is not a good match with
> LFP unless the user knows what they are doing. XW pro was made to close
> loop and communicate with the bms. Since there were no faults logged it
> sounds like the battery cut out before the XW LBCO, which is wrong as
> you know and this was fixed on XWpro. XW's should not change their
> master slave set-up unless they were really glitched or one has damaged
> memory. They should repower as they were set-up. Below is how it should
> look in set-up.
>
> Good Luck!
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> [1]https://offgridsolar1.com/ [2] [1]
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> On 2025-05-31 7:16 am, Jason Szumlanski via RE-wrenches wrote:
>
> Are they open on Saturdays? It doesn't really matter anyway because I
> went out to the remote island on an emergency basis this morning, and
> we have a big storm rolling in, so we had to hightail it out of there.
> I wouldn't have had time to call.
>
> I definitely intend to get in touch with them for any advice they might
> have. I was hoping to get some clues from anyone with similar
> experiences.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
> On Sat, May 31, 2025, 10:04 AM Jay <jay.peltz at gmail.com> wrote:
>
> Have you been able to get in touch with Schneider tech support?
>
> On May 31, 2025, at 7:45 AM, Jason Szumlanski via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> I have a new service client with dual XW+. When I first went out a
> couple of weeks ago, the LFP batteries had completely shut down due to
> low battery voltage. I had to jump start them with a Chargeverter. I
> discovered that the inverter low battery cutoff was 44 volts, which is
> lower than the battery BMS cut out. I also found the AGS set to manual
> off, and I believe the voltage triggers were defaults, but I am not
> certain.
>
> There is an AGS, SCP, two MPPT 60 150, one MPPT 100 600, and an Insight
> Home on the Xanbus Network. The owner cannot figure out how to access
> the Insight Cloud, and I could not access the device on the local
> network with the default password. Therefore, I am working with the SCP
> only for settings.
>
> I adjusted the settings on the inverters and AGS and checked all other
> settings. We tested the generator functionality. Everything seemed
> great.
>
> Fast forward to this week, and the system had a complete shutdown. I
> went out to the remote location today and found the inverters in
> standby. I tried to enable them, and received an F66 error. I dug in
> and found that they both had the same modbus address 00 and they were
> both set to split phase master. Everything else appeared to be factory
> defaults. Low battery cut out was sent to 44 volts again. The AGS had
> disappeared from the network on the SCP. The batteries were at 100%
> because the charge controllers were charging the batteries with solar
> for the last couple of days with no load present. After power cycling
> the inverters, the AGS reappeared on the SCP. The settings in the AGS
> were exactly as I had left them last time.
>
> It appears that the inverters went back to factory defaults, but
> everything else seemed okay.
>
> The only relevant thing in the fault logs was a low battery condition
> F48 fault that occurred six days ago. Then, 18 hours later, multiple
> F66 errors (5 or 6) occured over a 2-hour span. It appears this is when
> the inverters reverted to factory defaults.
>
> I don't work on a lot of Schneider inverters, so I am looking for any
> insights, no pun intended, that you may have about this behavior.
>
> I changed the names of the inverters from the factory default in the
> SCP. If the settings do revert to factory defaults again, I'm hoping
> this will be an indication if the names also revert.
>
> One more piece of information. I seriously doubt that the occupants of
> the property messed with anything in the SCP. However, I strongly
> believe that they were flipping breakers, particularly on the solar
> charge controllers. It's possible that turning off a controller messed
> up the Xanbus, but I don't see what that would have to do with settings
> getting changed.
>
> Jason Szumlanski
> Florida Solar Design Group
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250531/afd76909/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 0f1ba397.jpeg
Type: image/jpeg
Size: 38011 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250531/afd76909/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: b3342044.jpeg
Type: image/jpeg
Size: 10376 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250531/afd76909/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: dde7b80a.jpeg
Type: image/jpeg
Size: 11613 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250531/afd76909/attachment-0002.jpeg>
More information about the RE-Wrenches
mailing list