[RE-wrenches] Midnite AIO Generator Functionality
Jason Szumlanski
jason at floridasolardesigngroup.com
Wed May 14 12:49:31 EDT 2025
I will be using a Chargeverter tomorrow to dark start a set of Pytes. I
like the idea of including one of these with every system if the customer
will pony up the money.
I'm worried that development of the existing AIO is going to take a
backseat to the development of a new US-made model, which could take a
significant amount of time to bring to market. I'm hoping MNS we'll
continue to make improvements and fix some of these deficiencies.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Wed, May 14, 2025, 12:20 PM Maverick Brown via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> In the case of extra redundancy, I have installed the EG4 Chargeverter and
> a 30A L14-30 Inlet and made the customer a suitable length L14-30 Extension
> Cord that they can use with their manual start secondary / tertiary
> portable generator just in case the primary generator has failed to start.
> The Chargeverter is quite small and can handle about 5kW of charge just in
> case… The charge voltage is programmable as is the current. It is inverter
> and battery agnostic.
>
> The Chargeverter used to be inexpensive compared to what it does. The last
> time I checked it is over $700 and also always seems to be on backorder.
> Still worth it. The Chargeverter has two wire start and can start based on
> voltage and SOC (if that is where the batteries are communicating / not
> that useful for most cases).
>
> If the Chargeverter is the primary generator AC to DC Charger, all AIO
> inverters could benefit from DC Generator = Y / N setting. Reference :
> Available setting on XW and Outback.
>
> For that matter, I am sure there are other suitable chargers that can be
> added as an emergency spare. Ten years ago or more, I added an IOTA charger
> to 24V FX inverter so the customer could use their Honda 2000 to charge the
> battery without the warbling electricity going into the house because FX
> sans PF correction… Remember those fun days?
>
> Grid
> > Inverter / Battery / Solar
> >> Generator
> >>> Generator
> >>>> Candles
>
>
> [image: IMG_0168.jpeg]
>
>
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> *Maverick Solar Enterprises, Inc.*
> * • Solar Commander Remote Power*
>
> * • SunFlow Systems Cathodic Protection *maverick at mavericksolar.com
> 512-460-9825
>
> On May 14, 2025, at 8:55 AM, Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> That is the idea, but the generator startup is not guaranteed (i.e.out of
> fuel, battery dead, etc). It's not a failsafe solution.
>
> The AIO really needs a dedicated GEN input that is not controlled with a
> NO relay. Or let us use the Grid input for the generator. The generator
> input logic is severely flawed. If there is an AC source, it should be able
> to charge the battery without user intervention.
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
> On Mon, May 12, 2025, 5:25 PM Dave Tedeyan via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Jason,
>> Cant you just make the AGS turn on the generator before the inverter gets
>> to the LBCO? Maybe this is more difficult if you do not have closed loop
>> comms and the SOC drifts. I am just working through my first Midnite AIO
>> setup now, so I cannot speak to the nuances of how it will work with that
>> yet.
>> Cheers,
>> Dave
>>
>> On Mon, May 12, 2025 at 4:01 PM Ray Walters via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> That has not been my experience. I have had to manually reboot Solark
>>> systems numerous time off grid. If there is snow on the array or otherwise
>>> low PV output for a few days, the no load draw of the BMS then takes the
>>> battery voltage low enough to shut the battery off. This would be a
>>> different situation with a knowledgeable owner onsite full time, but for
>>> vacation properties, it will go into complete shut down, not coming back.
>>>
>>> Which gets into the manual and tech support for Solark: its really not
>>> clear what the different settings do, and how they interact. I'm sure
>>> there are engineers that know, but they aren't at Tech support. At least
>>> you can change the programming on the touch screen, and you don't have to
>>> get a quirky app up off grid to do basic changes.
>>>
>>> BTW, what happens when the developers quit keeping the App updated, 10
>>> years from now, and you can't access the programming? Planned
>>> Obsolescence? That 33 yr old Trace Inverter is still doing its job.....
>>>
>>> Ray Walters
>>> Remote Solar
>>>
>>>
>>>
>>> On 5/12/2025 11:33 AM, MDElectricSolar via RE-wrenches wrote:
>>>
>>> We have been using the Solark inverter for GTBB and off grid clients. In
>>> the case of low battery cut out the solar does stay alive in the background
>>> and will recharge the batteries when the sun comes out the next day and
>>> turn itself back on and provide AC power output.
>>>
>>> Michael D Nelson
>>> MD Electric & Solar, Inc.
>>> 707-684-0064 mobile
>>> 707-884-1862 office
>>> www.mdelectricsolar.com
>>> www.facebook.com/mdelectricandsolar
>>>
>>>
>>> On May 12, 2025, at 10:13 AM, Ray Walters via RE-wrenches
>>> <re-wrenches at lists.re-wrenches.org> <re-wrenches at lists.re-wrenches.org>
>>> wrote:
>>>
>>>
>>>
>>> So the bypass switch gets the house power on, and I too always recommend
>>> a hard bypass switch. However, you still need a 48 v power supply to get
>>> the battery system back up, and that's becoming a serious pain in my aging
>>> backside. Until AIOs with Li+ batteries, lead acid would have enough
>>> voltage to get the charge controller to come back on, and eventually the
>>> customer could get the inverter back on too. No special trip out.
>>>
>>> We need an independent circuit that would sense array voltage, and wake
>>> up the battery, so it could take a charge: a backup battery for the offgrid
>>> battery. Without that, AIOs and Li+ batteries are not self healing like
>>> Lead Acid. We are going backwards fast, but with an amazing amount of new
>>> Chinese technology driving the jalopy in reverse. (Danger Will Robinson)
>>>
>>> Ray Walters
>>> Remote Solar
>>> On 5/12/2025 10:54 AM, Jason Szumlanski via RE-wrenches wrote:
>>>
>>> We always recommend a transfer switch to bypass the inverter and send
>>> generator power to the loads. Most clients take us up on it. For retrofits,
>>> sometimes there can be space limitations, however.
>>>
>>> As for the function of the AIO, there is no integrated mechanical
>>> bypass, and since there is an internal relay controlling the
>>> generator input (or smart load output on that breaker), I think the default
>>> function is for the relay to open when the inverter turns off. AC voltage
>>> on the load side of the breaker does not close the relay and turn the
>>> inverter back on automatically.
>>>
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>> On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via
>>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> All sounds wrong to me. Call Midnite.
>>>>
>>>> Typically there is a AC bypass mechanical switch that allows the gen to
>>>> bypass the inverter and power loads.
>>>>
>>>>
>>>>
>>>> *Dave Angelini Offgrid Solar
>>>> "we go where powerlines don't"
>>>> <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
>>>> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
>>>> text 209 813 0060*
>>>>
>>>>
>>>> On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:
>>>>
>>>> Maybe I'm missing something, but it seems like there is a flaw in the
>>>> logic for how generator integration works with this product. Unlike some of
>>>> the other AIOs, you can't put the generator on the Grid input in an
>>>> off-grid scenario. You have to use the Generator smart load breaker, which
>>>> isn't a dedicated generator input, but a programmable circuit. This is
>>>> problematic because it seemingly has a normally open internal relay that
>>>> closes only when the inverter is ON. At least, that's how it seems to work
>>>> in my limited experience.
>>>>
>>>> Why is this a problem? If the battery capacity drops below the low
>>>> voltage cutoff, the inverter turns off. You have to turn the inverter ON
>>>> for the generator relay to close so you can charge the battery, but since
>>>> the battery is too low, the inverter won't turn on. You would have to
>>>> reprogram the inverter to drop the cutoff voltage/SOC below the current
>>>> battery state. For people who do not want to use AGS, or if AGS fails to
>>>> start the generator for any reason, getting the generator to charge the
>>>> battery manually is no easy task.
>>>>
>>>> Moreover, turning the generator on manually when the inverter is in an
>>>> OFF state will not pass power to the loads, and will not turn the inverter
>>>> ON automatically. You have to get the inverter turned ON somehow so that
>>>> the generator power can pass through to the loads. And since the startup
>>>> sequence for this inverter is very quirky, non-intuitive, and unreliable,
>>>> that makes the problem even worse. I'm not sure if you can even turn the
>>>> inverter ON when there is generator input and the battery is too low. I
>>>> don't think you can because the relay is open and the inverter doesn't even
>>>> see generator voltage when it is in an OFF state.
>>>> This seems like a serious oversight and a reason to go with one of the
>>>> other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV will both
>>>> immediately power loads and start charging when the generator is on,
>>>> regardless of whether the generator is connected to the Grid or Generator
>>>> input. Any AC input immediately passes through to the loads. This is
>>>> because those inverters stay "on" when a low battery condition is met, and
>>>> they simply stop using the battery to invert power if the battery
>>>> conditions do not allow it, based on the settings.
>>>>
>>>> The logic of the Midnite AIOs turning "off" when battery cutoff is met
>>>> and opening the generator relay doesn't make sense to me. Am I wrong about
>>>> how this works?
>>>>
>>>> Jason Szumlanski
>>>> Principal Solar Designer
>>>> Florida Solar Design Group
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250514/c126663f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IMG_0168.jpeg
Type: image/jpeg
Size: 93663 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250514/c126663f/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IMG_0168.jpeg
Type: image/jpeg
Size: 93663 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250514/c126663f/attachment-0001.jpeg>
More information about the RE-Wrenches
mailing list