I had many more failures with the VFX inverters, but at least we could 
rebuild them in the field.  I think the old Trace stuff was the pinacle 
of reliability.  I still have many SWs going well over 20 years.  I had 
great luck with Magnum, until I got my first dud last year.  Now they're 
out, but I'm installing a used one soon.

I'm really at a loss as to what to deploy at this point.  The AIOs are 
not the answer for offgrid, but I'm going to give a Midnite Rosie a try 
next, I think. I've been happy with Midnite's 600 v Charge Controllers, 
except don't use them on 24v!  (48v only)

I've tried some Victron stuff, which also requires a phone app and blue 
tooth to program.  Manuals could definitely use more info, and tech 
support has been non existent.  I use them for small projects (inverter 
< 2 kW) for now.

Ray Walters
Remote Solar

On 5/12/2025 9:52 AM, Drake Chamberlin via RE-wrenches wrote:
>
> Was Outback woes.
>
> Hi Ray,
>
> I agree completely. Off grid reached its peak reliability and then 
> declined. I thought it peaked with the VFX and Radian inverters, both 
> of which could have stood some improvements. With the VFXR and the 
> Radian A, The inverters seemed to be made more cheaply and more prone 
> to problems. The rest is history.
>
> The reliance on cell phones and internet seems to me to be completely 
> against the spirit of self reliant off grid systems. In the old days, 
> I would set up a system and after a bit (or lot) of messing around 
> would work for years.
>
> What is the best off grid inverter to use these days?
>
> Thank you,
>
> Drake
>
> /Drake Chamberlin/
>
> /Athens Electric LLC/
>
> /Ohio Electrical Contractor’s License 44810/
>
> /NABCEP Certified PV Installation Professional/
>
> ---
>
>
> On 2025-05-11 14:37, Ray Walters via RE-wrenches wrote:
>
>> I agree Michael, my call backs and free trips are way up with Li 
>> batteries and AIO.  I just don't know what the system is doing or 
>> what to expect from the settings.  Dark Start has now become a normal 
>> thing.  My blood pressure is off the charts trying to talk to tech 
>> support with one bar of cell service.  I have a DC power supply and 
>> inverter to restart the batts.  I now own a PC laptop that's sole 
>> purpose is firmware updates.
>>
>> Guess what? Lead acid almost never needed a trip out to restart.  The 
>> sun comes out, and it starts recharging. Lead acid is SELF HEALING. I 
>> just can't get LVD settings that keep Li bats out of dark start 
>> territory.  All is fine until its not.  Here's some experiences:
>>
>> 1) A Fortress firmware glitch that shut the whole system down when it 
>> reached 100% SOC.
>> Result: rotten food in both freezers, customer confidence: they sold 
>> the property.
>> Solution: upgrade Fortress Firmware.
>>
>> 2) Simpliphi and XW system works fine for 5 years, then a low battery 
>> issue during bad weather causes all 4 Simpliphi batteries to fry.
>> Result: customer is on generator full time for 2 months.
>> Solution: finally get replacement batteries and replace XW inverter 
>> with Magnum.
>>
>> 3) Homegrid batteries go into dark mode after solar shuts off for a 
>> couple of days.  No battery voltage to turn on charge controller 
>> again.  Result: 3 trips out to restart batteries, and hang out for 
>> hours to make sure the inverter will reconnect, and stay connected.
>> Solution: still not sure, I raised the LVD and reconnect voltages, 
>> but the battery's no load draw from the BMS seems to be very 
>> significant.
>>
>> 4) Midnite AIO won't connect to phone app, which is the only way to 
>> program it.  I turn on the inverter, and it just bricks.
>> Result: It can't function out of the box without being setup with the 
>> phone app that doesn't always work.
>> Solution: after 2-1/2 hours on a bad connection with Tech support, we 
>> finally get the inverter to reset and start working properly.  I had 
>> to delete and reload the phone app 5 times before it would finally 
>> connect to the inverter.   What's going to happen when you come back 
>> in 5 years with a different phone?
>>
>> I can share more with other companies I've tried including Rubix, and 
>> Blue Planet.  The only Li battery I've not had trouble with was LiFe 
>> Blue (thanks Larry), but they're only for 12v systems.   I am still 
>> installing lead acid for many of my customers, because we know what 
>> to expect. A lesser evil is better than the unknown that can be much 
>> worse.  Retirement can't come too soon.
>>
>> Ray Walters
>> Remote Solar
>>
>> On 5/11/2025 9:47 AM, Michael Morningstar via RE-wrenches wrote:
>>> I wonder where all this is going? A plethora of Chinese ( I 
>>> understand virtually everything electronic is manufactured there) 
>>> AIOs and batteries, each with their own communication protocols, 
>>> programing parameters, and individual peculiarities. I say this with 
>>> all modesty and humility, that until a few years ago, it was a rare 
>>> troubleshooting situation that I needed guidance from tech support 
>>> for most anything. Now the extent of my prowess has been reduced to: 
>>> "power cycle" it and if that doesn't work call tech support, and 
>>> then be prepared for a frustrating, protracted, and costly in terms 
>>> of my time, experience.
>>> I also wonder if it's sort of a "race to the bottom" (thanks for 
>>> that one Bob-O) as far a quality goes. Discover discontinued it's 
>>> AES battery which I think was the pinnacle, and replaced it with the 
>>> Helios (which I have high hopes for). I'm hoping it's not a clone of 
>>> all the others that are similar and I understand that the AES simply 
>>> couldn't compete.
>>> Just my mind dump sans edit
>>>
>>> On Sun, May 11, 2025 at 8:17 AM Jay <jay.peltz at gmail.com 
>>> <mailto:jay.peltz at gmail.com>> wrote:
>>>
>>>     Fortress and eg4 both use the same basic LUX made inverters.
>>>     Sol ark is made by DEYE.
>>>
>>>>     On May 11, 2025, at 8:04 AM, Michael Morningstar via
>>>>     RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>>     <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>
>>>>     How does the Lux, Envy, and Sol-Ark compare to Midnite's AIO? I
>>>>     was all on board the Midnite train but I'm coming to the
>>>>     conclusion that they released it prematurely. Glitchy and Quirky.
>>>>
>>>>     On Sun, May 11, 2025 at 7:40 AM Jay via RE-wrenches
>>>>     <re-wrenches at lists.re-wrenches.org
>>>>     <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>
>>>>         One of the things I like about the LUX is that you can do
>>>>         programming with the built in display.
>>>>         The online monitoring is good as Maverick says.
>>>>         I also think it's way more accurate as well.
>>>>         The LUX 12kw is a solid unit.
>>>>         Jay
>>>>
>>>>>         On May 11, 2025, at 7:35 AM, Maverick Brown via
>>>>>         RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>>>         <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>>
>>>>>         William,
>>>>>         I have both the ENVY and Radian (and XW at my own home).
>>>>>         The ENVY online experience is great. It may have replaced
>>>>>         the Sol-Ark online monitoring as my favorite. (I have
>>>>>         installed about 20 Sol-Arks and they also have tons of
>>>>>         data and a great overall online experience).
>>>>>         The data collected by ENVY is far greater than OpticsRE,
>>>>>         many more parameters are saved. ENVY also has a working
>>>>>         smart phone App that shows more data than the now offline
>>>>>         / defunct OpticsRE app.
>>>>>         OpticsRE does log enough data to understand that the
>>>>>         system is functioning, but the additional AC data and way
>>>>>         the information is presented gives ENVY far superior
>>>>>         results. I do lean more towards the way OpticsRE allows
>>>>>         editing parameters on the Devices section. That's likely
>>>>>         because I am more familiar with the terminology. But, The
>>>>>         ENVY Inverter has a built in display / touch screen that
>>>>>         allows you to edit all of the values and make the system
>>>>>         work without any internet / wireless / bluetooth
>>>>>         connection. That is a great fall back. I am used to the
>>>>>         MATE3s, but new customers have a crazy time with learning
>>>>>         how it works and where values are able to be changed. The
>>>>>         ENVY App bridges that gap!
>>>>>         Now the dream part is that since Outback is now owned by
>>>>>         the same people that also sell the EG4 18kPV (which is
>>>>>         also made by Luxpower just like the ENVY), the best of
>>>>>         both worlds could come about == more data collected and an
>>>>>         available and a solid smart phone app for customers that
>>>>>         want such a thing.
>>>>>         The screenshot of the app is straight forward and the tabs
>>>>>         at the bottom show charts, alarms and settings.
>>>>>         The screenshot for desktop is very detailed and you can
>>>>>         scroll down on the first page and get 3-4 screenfuls of
>>>>>         data for just about anything you want to know.
>>>>>         Let me know if you have a specific question, I can give
>>>>>         you a comparison.
>>>>>         <Screenshot 2025-05-11 at 9.11.09 AM.png>
>>>>>         <IMG_3420.PNG>
>>>>>
>>>>>         Maverick Brown
>>>>>         Off-Grid Solar Commander since 2006
>>>>>         *Maverick Solar Enterprises, Inc.*
>>>>>         * • Solar Commander Remote Power*
>>>>>         * • SunFlow Systems Cathodic Protection
>>>>>         *maverick at mavericksolar.com
>>>>>         <mailto:maverick at mavericksolar.com>
>>>>>         512-460-9825
>>>>>
>>>>>>         On May 10, 2025, at 9:58 PM, William Miller via
>>>>>>         RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>>>>         <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>>>
>>>>>>         Bought a VFXR3648 and two FXR3048s recently. They
>>>>>>         actually worked!  Miracle.
>>>>>>
>>>>>>         The client for which I am suggesting an Envy 12 instead
>>>>>>         of new FM100s is really attached to Optics. Now that
>>>>>>         Optics is unreliable it is easier to suggest an alternative.
>>>>>>         I'd like to hear about the Envy on-line interface. Is it ok?
>>>>>>
>>>>>>         William Miller
>>>>>>         Miller Solar.com
>>>>>>         805-438-5600
>>>>>>         www.millersolar.com <http://www.millersolar.com/>
>>>>>>
>>>>>>         On Sat, May 10, 2025 at 12:23 PM Jay via RE-wrenches
>>>>>>         <re-wrenches at lists.re-wrenches.org
>>>>>>         <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>>>
>>>>>>             As a follow up.
>>>>>>             Has anyone purchased a new OB inverter or CC or mate.
>>>>>>             I mean specifically remote new outback company.
>>>>>>             Jay
>>>>>>
>>>>>>>             On May 10, 2025, at 11:19 AM, Todd Cory via
>>>>>>>             RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>>>>>             <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>>>>
>>>>>>>             Well, Outback's Optics RE is down yet again, also
>>>>>>>             the back up site too and also the users forum...
>>>>>>>             which had a massive database of current and past
>>>>>>>             problem solving archives.
>>>>>>>
>>>>>>>             What a clusterfuck this new company is.
>>>>>>>
>>>>>>>             Wise wrenches should beware of patronizing this
>>>>>>>             obvious sinking ship.
>>>>>>>
>>>>>>>             Todd
>>>>>>>
>>>>>>>
>>>>>>>             <img-0.png>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>             Sent from Finest Planet WebMail.
>>>>>>>             <img-0.png>
>>>>>>>             _______________________________________________
>>>>>>>             List sponsored by Redwood Alliance
>>>>>>>
>>>>>>>             Pay optional member dues here:
>>>>>>>             http://re-wrenches.org <http://re-wrenches.org/>
>>>>>>>
>>>>>>>             List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>>             <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>>
>>>>>>>             Change listserver email address & settings:
>>>>>>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>             <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>>>
>>>>>>>             There are two list archives for searching. When one
>>>>>>>             doesn't work, try the other:
>>>>>>>             https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>>             <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>>>>>             http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>             <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>>>
>>>>>>>             List rules & etiquette:
>>>>>>>             http://www.re-wrenches.org/etiquette.htm
>>>>>>>             <http://www.re-wrenches.org/etiquette.htm>
>>>>>>>
>>>>>>>             Check out or update participant bios:
>>>>>>>             http://www.members.re-wrenches.org
>>>>>>>             <http://www.members.re-wrenches.org/>
>>>>>>             _______________________________________________
>>>>>>             List sponsored by Redwood Alliance
>>>>>>
>>>>>>             Pay optional member dues here: http://re-wrenches.org
>>>>>>             <http://re-wrenches.org/>
>>>>>>
>>>>>>             List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>             <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>>             Change listserver email address & settings:
>>>>>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>             <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>>
>>>>>>             There are two list archives for searching. When one
>>>>>>             doesn't work, try the other:
>>>>>>             https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>             <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>>>>             http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>             <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>>
>>>>>>             List rules & etiquette:
>>>>>>             http://www.re-wrenches.org/etiquette.htm
>>>>>>             <http://www.re-wrenches.org/etiquette.htm>
>>>>>>
>>>>>>             Check out or update participant bios:
>>>>>>             http://www.members.re-wrenches.org
>>>>>>             <http://www.members.re-wrenches.org/>
>>>>>>
>>>>>>         _______________________________________________
>>>>>>         List sponsored by Redwood Alliance
>>>>>>
>>>>>>         Pay optional member dues here: http://re-wrenches.org
>>>>>>         <http://re-wrenches.org>
>>>>>>
>>>>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>>         Change listserver email address & settings:
>>>>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>         <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>>
>>>>>>         There are two list archives for searching. When one
>>>>>>         doesn't work, try the other:
>>>>>>         https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>         <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>>>>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>         <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>>
>>>>>>         List rules & etiquette:
>>>>>>         http://www.re-wrenches.org/etiquette.htm
>>>>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>>>>
>>>>>>         Check out or update participant bios:
>>>>>>         http://www.members.re-wrenches.org
>>>>>>         <http://www.members.re-wrenches.org>
>>>>>>
>>>>>         _______________________________________________
>>>>>         List sponsored by Redwood Alliance
>>>>>
>>>>>         Pay optional member dues here: http://re-wrenches.org
>>>>>         <http://re-wrenches.org>
>>>>>
>>>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>>         Change listserver email address & settings:
>>>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>         <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>
>>>>>         There are two list archives for searching. When one
>>>>>         doesn't work, try the other:
>>>>>         https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>         <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>>>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>         <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>
>>>>>         List rules & etiquette:
>>>>>         http://www.re-wrenches.org/etiquette.htm
>>>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>>>
>>>>>         Check out or update participant bios:
>>>>>         http://www.members.re-wrenches.org
>>>>>         <http://www.members.re-wrenches.org>
>>>>         _______________________________________________
>>>>         List sponsored by Redwood Alliance
>>>>
>>>>         Pay optional member dues here: http://re-wrenches.org
>>>>         <http://re-wrenches.org>
>>>>
>>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>         Change listserver email address & settings:
>>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>         <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>
>>>>         There are two list archives for searching. When one doesn't
>>>>         work, try the other:
>>>>         https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>         <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>         <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>
>>>>         List rules & etiquette:
>>>>         http://www.re-wrenches.org/etiquette.htm
>>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>         Check out or update participant bios:
>>>>         http://www.members.re-wrenches.org
>>>>         <http://www.members.re-wrenches.org>
>>>>
>>>>     -- 
>>>>
>>>>     Michael Morningstar
>>>>
>>>>     Morningstar Electric Inc
>>>>
>>>>     PO Box 1494
>>>>
>>>>     Mount Shasta, CA 96067
>>>>
>>>>     530-921-0560
>>>>
>>>>     CSLB 1116835
>>>>
>>>>     mjmorningstar at gmail.com <mailto:mjmorningstar at gmail.com>
>>>>
>>>>     _______________________________________________
>>>>     List sponsored by Redwood Alliance
>>>>
>>>>     Pay optional member dues here: http://re-wrenches.org
>>>>     <http://re-wrenches.org>
>>>>
>>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>     Change listserver email address & settings:
>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>
>>>>     There are two list archives for searching. When one doesn't
>>>>     work, try the other:
>>>>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>     <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>>>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>     <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>
>>>>     List rules & etiquette:
>>>>     http://www.re-wrenches.org/etiquette.htm
>>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>     Check out or update participant bios:
>>>>     http://www.members.re-wrenches.org
>>>>     <http://www.members.re-wrenches.org>
>>>
>>> -- 
>>>
>>> Michael Morningstar
>>>
>>> Morningstar Electric Inc
>>>
>>> PO Box 1494
>>>
>>> Mount Shasta, CA 96067
>>>
>>> 530-921-0560
>>>
>>> CSLB 1116835
>>>
>>> mjmorningstar at gmail.com <mailto:mjmorningstar at gmail.com>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here:http://re-wrenches.org <http://re-wrenches.org>
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>
>>> There are two list archives for searching. When one doesn't work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try 
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250512/ff63b154/attachment.htm>


More information about the RE-Wrenches mailing list