[RE-wrenches] Midnite AIO Generator Functionality

Jason Szumlanski jason at floridasolardesigngroup.com
Mon May 12 12:54:14 EDT 2025


We always recommend a transfer switch to bypass the inverter and send
generator power to the loads. Most clients take us up on it. For retrofits,
sometimes there can be space limitations, however.

As for the function of the AIO, there is no integrated mechanical bypass,
and since there is an internal relay controlling the generator input (or
smart load output on that breaker), I think the default function is for the
relay to open when the inverter turns off. AC voltage on the load side of
the breaker does not close the relay and turn the inverter back on
automatically.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via RE-wrenches
<re-wrenches at lists.re-wrenches.org> wrote:

> All sounds wrong to me. Call Midnite.
>
> Typically there is a AC bypass mechanical switch that allows the gen to
> bypass the inverter and power loads.
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/>  <http://members.sti.net/offgridsolar/>
> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
>
> On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:
>
> Maybe I'm missing something, but it seems like there is a flaw in the
> logic for how generator integration works with this product. Unlike some of
> the other AIOs, you can't put the generator on the Grid input in an
> off-grid scenario. You have to use the Generator smart load breaker, which
> isn't a dedicated generator input, but a programmable circuit. This is
> problematic because it seemingly has a normally open internal relay that
> closes only when the inverter is ON. At least, that's how it seems to work
> in my limited experience.
>
> Why is this a problem? If the battery capacity drops below the low voltage
> cutoff, the inverter turns off. You have to turn the inverter ON for the
> generator relay to close so you can charge the battery, but since the
> battery is too low, the inverter won't turn on. You would have to reprogram
> the inverter to drop the cutoff voltage/SOC below the current battery
> state. For people who do not want to use AGS, or if AGS fails to start the
> generator for any reason, getting the generator to charge the battery
> manually is no easy task.
>
> Moreover, turning the generator on manually when the inverter is in an OFF
> state will not pass power to the loads, and will not turn the inverter ON
> automatically. You have to get the inverter turned ON somehow so that the
> generator power can pass through to the loads. And since the startup
> sequence for this inverter is very quirky, non-intuitive, and unreliable,
> that makes the problem even worse. I'm not sure if you can even turn the
> inverter ON when there is generator input and the battery is too low. I
> don't think you can because the relay is open and the inverter doesn't even
> see generator voltage when it is in an OFF state.
> This seems like a serious oversight and a reason to go with one of the
> other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV will both
> immediately power loads and start charging when the generator is on,
> regardless of whether the generator is connected to the Grid or Generator
> input. Any AC input immediately passes through to the loads. This is
> because those inverters stay "on" when a low battery condition is met, and
> they simply stop using the battery to invert power if the battery
> conditions do not allow it, based on the settings.
>
> The logic of the Midnite AIOs turning "off" when battery cutoff is met and
> opening the generator relay doesn't make sense to me. Am I wrong about how
> this works?
>
> Jason Szumlanski
> Principal Solar Designer
> Florida Solar Design Group
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250512/f133dac4/attachment.htm>


More information about the RE-Wrenches mailing list