[RE-wrenches] String fuse blown

david quattro david at quattrosolar.com
Fri Apr 11 15:48:02 EDT 2025


One time I had similar, but different problem:  1 Amp ground fault fuse
consistently blowing, sometimes after 1 day sometimes after weeks/months.
I tried everything - replaced home runs, checked VOC, VMP, swapped DC input
into a different inverter, etc. it kept coming back to this one string. I
checked every module VOC, ISC, every connection, no pinched wires, no
discernible problem, but fuse blowing.
   Luckily it was a medium size commercial job (on a fire station) so I was
able to scatter all the modules of this suspect string all over the roof,
and carefully track where I had put them. That’s when the problem went away
and never came back..😂
  Best I could figure was a slight manufacturing error that had a
compounding/cumulative effect. So once I got those consecutive serial
numbers away from each other no more problem. Either that or the fire chief
was fucking with me and he was burning out the fuses, which I doubt



On Fri, Apr 11, 2025 at 8:05 AM Mac Lewis via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hello Amos,
>
> Have you checked for voltage imbalance for each string?  If you have a bad
> diode, that string may run low on voltage and be trying to send current
> toward the weak string (this is the reason you have these breakers).  I'd
> run each string independently and see what Vmp is.  If you are missing some
> voltage that may be a clue.  You can also independently clamp each string
> during operation.
>
> I like IR cameras for this type of thing.  It may just be a bad
> connection, heat build up, fuse holder issue.
>
> Let us know what you find out
>
> On Fri, Apr 11, 2025 at 8:07 AM Amos Post via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hi Wrenches,
>>
>> I have a bit of a puzzler that I’m trying to get sorted out.  I’ve been
>> servicing a Grid-Tied Battery Backup system that’s about 17-18 years old.
>> The system comprises of 2-GVFX3648s in series, with 2-MX60(at least I think
>> they are 60s) CC’s.  Each CC has 3 strings of 3 tied to it, and each string
>> has a 15A in-line 600V fuse.  The modules are I believe are like
>> 230/240Watt 60 cell modules (sorry I don’t have pictures/specifics).   We
>> replaced the flooded batteries with AGMs about a year and a half ago.
>>
>> The situation is one of the 15A string fuses keeps blowing.  It’s now
>> happened 3 times and its the same fuse every time.  First we just replaced
>> the fuse and under the surge/lightning assumption.  Fuse blew again.  Then
>> I thought I found the culprit.  The #6 PV output from the combiner to the
>> PV input breaker for the CC was a bit darkened and very warm to the touch
>> when I replaced the fuse the first time.   So I though maybe it was a loose
>> connection on that lug and that caused everything to heat up and eventually
>> blow the fuse.  I cut and stripped the wire back and cleaned the lug and
>> re-seated the wire in the lug.  Fuse blew again within a few months time.
>> I then checked the Junction box on the roof where the USE-2 wire connects
>> to THHN, and did a visual inspection of all the wiring on the roof.  All of
>> the Jbox connections and everything on the roof “looked” ok.  I have also
>> check all of the connections inside the Outback DC load center, and they
>> look ok.  Fuse replaced 3rd time and then it blew again.
>>
>> Before I take all of the panels off the rack, check panels, re-check
>> string wiring on the roof, is there anything else I should be checking?
>> Seems like that warm wire in the Combiner box is telling me something but I
>> can’t figure out what...I believe this is a new problem in the last 2-3
>> years but we are not 100% sure when the problem first came up…
>>
>> As always, thanks for your help/ suggestions!
>> Amos
>>
>>
>>
>>
>>        Amos Post
>>    Integrity Energy
>>   W 802.763.7023
>>    C 802.291.2188
>>     ienergyVT.com <http://www.ienergyvt.com>
>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250411/06262c5a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IE LOGO 150x78.jpg
Type: image/jpeg
Size: 7516 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250411/06262c5a/attachment.jpg>


More information about the RE-Wrenches mailing list