[RE-wrenches] Class 320 meter main combos, new requirements
William Miller
william at millersolar.com
Thu Mar 27 19:14:49 EDT 2025
Friends:
I have ordered a Class 320 Meter/Main/Combo. My vendor informs me there
are new codes that apply to these cans, specifically in 230.71(B), cited
below:
*(B) Two to Six Service Disconnecting Means. *Two to six service
disconnects shall be permitted for each service permitted by
230.2 or for each set of service-entrance conductors permitted
by 230.40, Exception No. 1, 3, 4, or 5. The two to six service
disconnecting means shall he permitted to consist of a combination
of any of the following:
(1) Separate enclosures with a main service disconnecting
means in each enclosure
(2) Panelboards with a main service disconnecting means in
each panelboard enclosure
(3) Switchboard(s) where there is only one service disconnect
in each separate vertical section where there are
barriers separating each vertical section
(4) Service disconnects in switchgear or metering centers
where each disconnect is located in a separate compartment
Here is an analysis, apparently from Siemens:
Apparently there are factory partitions required now and some models have
them and some do not. Of course the one I specified, advocated for and
that is cheaper does not have the partition. I don’t want to order the
wrong one so I am looking for verification I am understanding this
correctly.
Have any of you run up against this when ordering these devices or having
them approved?
Thanks in advance for any input!
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250327/81bf7267/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 91318 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250327/81bf7267/attachment.png>
More information about the RE-Wrenches
mailing list