[RE-wrenches] Automatic Dark Start of Depleted Lithium Batteries
Steve Higgins
steve at surrette.com
Sat Feb 22 11:45:02 EST 2025
Thanks, Darryl... I'm not that smart, If I were I'd be retired by now!!!
I'm just relating what I've seen over the past three decades...
On Sat, Feb 22, 2025 at 8:35 AM Darryl Thayer via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Would you be able to do this with the Morningstar relay driver? The relay
> closes and starts the generator when the battery voltage reaches a certain
> level. The following is an inferior idea; use an Egauge in particular if
> you want to do other monitoring, and have the Egauge with a relay driver
> close the generator start switch.
>
> Also, pay attention to Steve Higgens Ideas
>
> On Sat, Feb 22, 2025 at 7:08 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> I have been thinking a lot recently about the reasons off-grid systems
>> can shut down, and working on strategies to prevent these nuisances that
>> require manual intervention.
>>
>> Ideally, a BMS should never shut down due to low voltage/SOC because a
>> properly programmed inverter should reach it's cut off well before the BMS
>> decides it needs to protect the battery, especially where there is closed
>> loop communication. But let's say that happens, where the BMS does make the
>> DC battery output go to zero.
>>
>> It seems to me like the inverter should be able to start a generator, and
>> then signal to the BMS that a charging source is available. But I'm not
>> aware of any system that actually does this. The inverter should be able to
>> wake up the battery. I can see this being particularly possible where one
>> manufacturer is writing the code (I'm thinking Midnite AIO/Powerflo).
>>
>> Of course, the inverter would have to have power in order to do that, so
>> if it's nighttime and there is no PV, the inverter power would need to come
>> from somewhere. I have two thoughts. First, someone could manually start
>> the generator, waking up the inverter, but they would not have to reset the
>> BMS if the inverter told it to wake up. The second way would be for the
>> inverter to somehow close the 2-wire start circuit upon inverter shutdown,
>> restoring power to the inverter automatically.
>>
>> If those are not options, an external NO relay powered by the inverter
>> output could be added to the 2-wire start circuit, perhaps with a time
>> delay to return to the NO position to allow the generator to remain powered
>> until the inverter does it's thing and starts charging the batteries.
>>
>> Anyway, my question is whether any inverter/battery combination out there
>> works in a way that the inverter tells the battery there is a charging
>> source available to wake up the BMS and reconnect DC power. And if not, why?
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250222/d1cc27c5/attachment.htm>
More information about the RE-Wrenches
mailing list