Around here, AHJs require that the GEC is not connected to the service
disconnect or any supply-side interconnected PV AC disconnect. They require
a GEC from the meter socket enclosure to the GE system with a N-G bond in
the meter enclosure (the N and G lugs are one and the same typically anyway
in a meter enclosure). The GEC must be continuous or irreversibly spliced
from the meter socket to the ground rods or a confirmable ufer ground or
other approved GE system.

The service disconnect is connected to the meter socket lugs with L1, L2,
and N with no equipment grounding conductor, although in many
circumstances, the meter enclosure is electrically bonded to the service
disconnect enclosure if a metallic raceway is used. The service disconnect
is bonded (N-G). And supply side interconnected disconnects only have L1,
L2, and N with no EGC, and they are also bonded.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Wed, Feb 19, 2025 at 10:53 PM Corey Shalanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Kris,
>
> As far as I know, taps to GECs need not be irreversible. I believe you
> might be thinking of the NEC 250.64(C) requirement for GECs to be installed
> "in one continuous length" or otherwise be spliced together via one of
> several options, with one option being to use irreversible compression-type
> connectors—but I'm pretty sure that refers to *individual* GECs (as in,
> *each* GEC must either be run continuous or can be pieced together via
> irreversible means).
>
> It sounds like your scenario is a supply-side connection, which introduces
> an additional service equipment enclosure in the form of the PV system
> disconnect (additional to any existing service equipment) and would
> therefore be covered by NEC 250.64(D). One option, described in (D)(2),
> would be to run a new GEC from the PV system disconnect directly to the
> (existing) grounding electrode system. The other option*, described in
> (D)(1), is to run a GEC "tap" from the PV system disconnect to a "common"
> GEC. In cases where there is only a single existing service equipment
> enclosure - and therefore only a single existing GEC - my interpretation is
> that the existing GEC can serve as the common GEC (essentially doing double
> duty as a "common/tap" GEC, if it helps to think of it that way) and you
> can therefore connect the new GEC tap directly to it. Notably, this method
> allows for the use of "connectors listed as grounding and bonding
> equipment"—we commonly use split bolts for the purpose.
> *There is also a third option [(D)(3)], but, in my experience, it is
> uncommon to have wireways on the supply side of service disconnects.
>
> So, I would suggest there is no need to use compression connectors - but
> you can certainly do so as an 'above-Code' measure.
>
> Corey Shalanski
> Cherry Street Energy
> Atlanta, GA
>
>
> On Wed, Feb 19, 2025 at 8:18 AM Kristopher Schmid via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hi All,
>>
>> What are you all using for an "irreversible" tap to an existing GEC?  I
>> have been looking at compression CTAPs.  Do they require a special crimper
>> die?
>>
>> Thanks,
>> Kris
>>
>>
>> Shine On!
>>
>> Kris Schmid
>> Legacy Solar, LLC
>> 137 West 1st Avenue
>> Luck, WI 54853
>> www.legacysolar.com
>> 715-653-4295
>> NABCEP Certified PV Installation Professional
>> Licensed Wisconsin Master Electrician
>> BSEE
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250220/0d596213/attachment.htm>


More information about the RE-Wrenches mailing list