David:

Fascinating and to the point. Your narrative begs the question:  What is
that nickname?

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Tue, Feb 18, 2025 at 5:16 PM David Buckner via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> We are either using Solar Edge or designing and procuring to UL3741 to
> meet rapid shut down without MLPE.  Be careful cost wise with larger roofs
> where the AC runs from inverters that are far away and next to their
> subarray are resulting in larger wire sizes.  Still, it’s worth it to sleep
> a little better at night.
>
>
>
> The manufacturers of MLPE’s were justifiably not ready to deliver safe
> products to the industry at the scale needed.  Is there a product that will
> safely last 25 years under these conditions?  90+ degrees on the roof that
> day and 20 degrees out there today.  I always remember John Wiles saying
> forget about the modules working for 25 years, worry about the BOS.  And
> for the most part that’s generally accurate.
>
>
>
> In our specific fire last year:
>
>    1. Firefighters didn’t go on the roof (and they apparently do not in
>    such situations here) but rather sprayed it from two separate locations.
>    2. Firefighters didn’t shut off the solar AC disconnect which was
>    external and accessible.  Eventually it was shut off by the owner when they
>    realized the system was still operating.
>    3. The next morning when the sun came up and the damaged array started
>    arcing and burning, they sprayed it for another couple of hours.
>    4. After a structural engineer inspected the decking, we were finally
>    allowed on the roof to make the situation as safe as possible electrically
>    which consisted of isolating down to every module in damaged areas and
>    every string that wasn’t damaged.  Otherwise the damaged RSDs weren’t
>    making anything safer.
>    5. Investigation by multiple insurance companies’ fire expert teams
>    followed but not for two weeks.
>    6. The teams knew each other from chasing these types of fires across
>    the country and they had a nickname for the RSD on this roof.
>    7. $3M in damage was the last number I heard.  Thankfully no immediate
>    injuries, other than psychological, but that smoke is absolutely horrible.
>    8. Here is a link to the fire:
>    https://www.google.com/search?q=roof+fire+secaucus+NJ&rlz=1C1ASVC_enUS948US955&oq=roof+fire+secaucus+NJ&gs_lcrp=EgZjaHJvbWUyBggAEEUYOTIHCAEQIRigATIHCAIQIRigATIHCAMQIRigATIHCAQQIRigATIHCAUQIRirAtIBCDUwNjZqMGo0qAIAsAIB&sourceid=chrome&ie=UTF-8#fpstate=ive&vld=cid:2ee587e2,vid:7Vw-5alnbKM,st:0
>
>
>
> We’re seeing insurance companies sending questionnaires out to our PV
> system owners asking about maintenance agreements, type of equipment, etc.
> One of the questions inevitably is whether there are module level shut down
> devices installed.  I wonder who is helping them out with that
> questionnaire.  And at some point will the presence of MLPE’s be viewed as
> positive or negative when writing the insurance policy for that building?
>
>
>
> David
>
>
>
>
>
> David Buckner​​​​
>
> President
>
> Solar Energy Systems
>
> 917-848-0215
>
> 718-389-1545
>
> dbuckner at solaresystems.com
>
> www.solaresystems.com
> <https://us.content.exclaimer.net/?url=https%3A%2F%2Fwww.solaresystems.com%2F&tenantid=sjl0rdWaEe6F-WBFvdNAXQ&templateid=933619bad6e2ee11aaf06045bdd55b16&excomponentid=W0znjuLBICxfJOZwpEisk1w6Uz7kRcz8RFh31bsCZu4&excomponenttype=Link&signature=oLHGWCDHeQYPxuVijopczXguVIz2A9gWA29emAtwvdbqV2XsAnsbVfPJR3OQHtcxck-4zeNWEHrxwAX_LXCUOBXnvLDZkSB3Ue09sLzQcUNKGxMLclBt5peel7iiM1neHKnk8UctTRnOeUfIagifjZaGWicP4Wi23eUaL-JSNh0iUlYWH5Y2kOEt_QGU-R6LtdhPzR8aNOqjq8ttGuksaSFX3YQorUNiBDkXDGXmmCSiiNgljGMekvYiEvoXMsCe_CC1DpnfHsaH45ZBD8L442uACHbkOuyDJ-IG20zpBYXGK3TzDh-GW4efLwZfi6MUcJohrIgQQag5JDhSynWoDQ&v=1&imprintMessageId=2334a7e3-dde4-4a79-bd85-9343a7155fa9>
>
> 41
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  Box
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  Street
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  2nd
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  Floor,
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  Brooklyn,
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  NY
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>  11222
> <https://www.google.com/maps/search/41+Box+Street+2nd+Floor,+Brooklyn,+NY+11222?entry=gmail&source=g>
>
> The information contained in this email message, including any attached
> files transmitted, is confidential and may be legally privileged. It is
> intended for the sole use of the individual(s) named above. If you are the
> intended recipient, be aware that your use of any confidential or personal
> information may be restricted by state and federal privacy laws. If you,
> the reader of this message, are not the intended recipient, you are hereby
> notified that you should not further disseminate, distribute or forward
> this email message. Email transmission cannot be guaranteed to be secured
> or error-free as information could be intercepted, corrupted, lost,
> destroyed, arrive late or incomplete, or contain viruses. The sender
> therefore does not accept liability for any errors or omissions in the
> contents of this message, which arise as a result of this e-mail
> transmission. If you have received this email in error, please notify the
> sender and immediately delete the material from your computer system. Thank
> you.
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Rebekah Hren via RE-wrenches
> *Sent:* Monday, February 17, 2025 1:26 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Rebekah Hren <rebekah.hren at gmail.com>
> *Subject:* Re: [RE-wrenches] RSS: Is it necessary?
>
>
>
> CAUTION: External Email.
>
> I read the wrenches post regularly, as does Brian Mehalic. We have both
> been on CMP-4  (responsible for Article 690) for the past three code
> cycles. I believe a few other CMP members probably read too. The
> International Association of Firefighters ("largest and most influential
> labor unions in North America") is represented on CMP-4 and yes they do
> have had a lot to say about this issue.
>
>
>
> This is definitely not the first time we have heard that certain RS
> devices are on balance causing more trouble than they are curing  - though
> on the other hand some manufacturers have certainly figured out how to make
> safe and effective MLPE.
>
>
> I'm a big fan of UL3741, I have been on that UL technical committee for
> about 5 years, and it is the best approach I see to expand both off-grid
> and grid-interactive solutions that don't require MLPE for RS. SMA for
> example is very present and working hard at revisions on that standard
> right now. At this point I can't see us having any luck in removing 690.12
> requirements, except perhaps to replace the inside the array boundary
> voltage limit with only option as 3741 listing). So please keep asking
> manufacturers (inverter/rack) to pay attention to UL3741 and design
> products to meet the standard.
>
>
>
> Best
>
> Rebekah
>
> Licensed Electrical Contractor
> NABCEP Certified Solar PV Installation Professional™ 091209-85
>
> Tel: 336.266.8800
>
>
>
>
>
> On Mon, Feb 17, 2025 at 10:59 AM Amos Post via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Seems like there has been talk of rescinding RSD requirements before on
> this forum.  It also seems that it might gain some traction if a dedicated
> group of installers spoke up to the right people (Code Making Panel for
> instance) and put some time into it.   I agree that at the very least we
> need reliable RSD equipment, and my preference would be less vs more.
>
>
>
> Does anybody know if any sort of RSD is being required in Europe (not that
> we follow their electrical codes/ideas…just curious)???
>
>
>
>
>
>
>
>        Amos Post
>    Integrity Energy
>   W 802.763.7023
>    C 802.291.2188
>     ienergyVT.com <http://www.ienergyvt.com/>
>
>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>
>
>
> On Feb 17, 2025, at 12:30 PM, david quattro via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> It seems anecdotal until it happens to you.
>
>     My mention of civil disobedience has been answered clearly with a “No”
> in this forum, and I'm fine to hear that.
>
>    I'll clarify a few points as to why I honestly think RSD has been a
> huge and costly mistake. I genuinely think RSD requirements should be
> terminated immediately. If the technology were more robust and if it worked
> consistently I wouldn't protest. But *all* the products I've tried have
> been trouble.
>
>    William, respectfully your analogy to seat belts is not an appropriate
> comparison to Rapid Shutdown. Seat-belts were required in all new cars
> starting in 1968 because there was statistical evidence supporting their
> tremendous efficacy in saving human life. Currently seat belts save about
> 15,000 lives per year.
>
>     Contrasting to RSD: was implemented because of the following paranoid
> fairytale scenario - “A firefighter is on a burning solar roof in the
> daytime, and wearing a metal axe at their hip. the poor guy/gal falls into
> live solar glass, and shatters it. The fall is so forceful that the
> heavy-duty fireman’s suit is punctured. Electricity conducts through the
> axe blade, through the suit, contacts the skin, and a DC circuit is
> completed through their body.”
>
>    As far as I know, this has never happened once anywhere on earth. Let’s
> be honest - this scenario has an incredibly low chance of ever happening in
> all the future of humanity. So considering that RSD has never helped anyone
> yet, and probably never will... How many fires can be attributed to RSD?
> How much property damage has occurred because of these fires?
>
>         The best path to safety for firefighters is by preventing fire
> disasters in the first place.  Fires spread. Any fire that happens
> endangers property owners, tenants, business owners, neighbors, shoppers,
> bystanders, nearby forests, etc.  RSD manufacturers aren't doing a good job
> right now, so we are seeing low quality unreliable electronics on the roof.
> I will stick my neck out and admit that installers are not always perfect.
> Humans make mistakes - sometimes in initial construction, and sometimes
> during repair and maintenance (i.e. when hunting down failed RSD's which
> happens far more than it should).
>
>    At this time, these devices are not being designed to withstand
> reality. When problems happen, manufacturers are quibbling. They ignore you
> until you go away, or until you sue them.
>
>     This level of "safety" is not important, and in fact RSD is causing
> fires every year.
>
>
>
>
>
>
>
>
>
>
>
> On Sat, Feb 15, 2025 at 11:38 AM William Miller <william at millersolar.com>
> wrote:
>
> David, Ray:
>
>
>
> I have not had any problems with the Tigo RSS equipment I have installed
> and I have had minimal problems with optimizers and micro-inverters (which
> are also RSS equipment).  Apparently others have had failures.  We don’t
> know statically how serious this problem is—the posts here are purely
> anecdotal.
>
>
>
> We also have not heard from the other side of the debate: the fire
> fighters.
>
>
>
> Based on lack of verifiable information I can not personally conclude that
> RSS is all problem and no benefit.
>
>
>
> To declare that the concept is flawed because the equipment available is
> not reliable is like saying we should not be required to install airbags
> because a bad batch of them was manufactured.  We are seeing problems with
> the equipment needed to implement a safety requirement.  That observation
> does not logically conclude the safety requirement is not valuable.
>
>
>
> I hesitate to dismiss any safety requirement out of hand.  Safety systems
> are designed to save lives and protect from injury, and most of them do.  I
> am glad to have anti-lock brakes, smoke detectors and air bags.   I have
> also found it quite handy to initiate RSS to allow me to work more safely
> on solar circuits.
>
>
>
> Does anyone on this installers forum have contacts in the fire-response
> community that can comment on the their side of the issue?  If RSD is
> really necessary for safety, then I will do my best to install good
> equipment properly and hold manufacturers accountable for shoddy
> solutions.  If RSD is not that effective we need to discuss undoing the
> code requirements.
>
>
>
> Sincerely,
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *david quattro via RE-wrenches
> *Sent:* Saturday, February 15, 2025 6:05 AM
> *To:* RE-wrenches
> *Cc:* david quattro
> *Subject:* Re: [RE-wrenches] Tigo inverter experience
>
>
>
> RSD is the worst thing to happen to solar. Has anyone considered civil
> disobedience?
>
>     I wonder what would happen if all the installers banded together and
> refused, as a united industry ‘brotherhood.’ WE are the ones stuck with the
> bullshit in the aftermath.
>
>      I’m not being snarky here , this a genuine question to the group:
> Does anyone have *good* experience with RSD?   i.e. you’re really glad
> RSD was there, and you genuinely feel safer?  you’re glad and happy to
> comply with this code and you look forward to continuing to use RSD for the
> rest of your career?
>
>
>
>
>
>
>
>
>
> On Fri, Feb 14, 2025 at 3:40 PM Ray Walters via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> it seems silly that we are required to install these extra pieces of
> equipment for added "safety", that are actually a fire hazard on the roof.
> Just to survey again: how many homes have been saved by RSD?  How many fire
> fighters have actually actuated the RSD system, so that they could hack
> through the array to vent the roof?
>
> I think it should only be required if you have covered so much of the roof
> with PV, that the fire dept can't access uncovered roof to do their
> venting.  The whole premise of RSD is flawed.  IMHO, its just another
> effort to block the wider adoption of solar.
>
> When it comes to off grid, RSD causes such a decrease in reliability to
> amount to a decrease in safety, due to possible loss of communications,
> water, and heat.  Add the fire hazard and RSD is really not making our
> customers' lives better.
>
> Ray Walters
> Remote Solar
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image088630.png
Type: image/png
Size: 40037 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image489307.png
Type: image/png
Size: 608 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image645183.png
Type: image/png
Size: 402 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image992640.png
Type: image/png
Size: 804 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 7516 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image243506.png
Type: image/png
Size: 499 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image797515.png
Type: image/png
Size: 596 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/4dff8e47/attachment-0005.png>


More information about the RE-Wrenches mailing list