On Tue, Feb 18, 2025, 2:24 PM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Yes, but the PV system would need to be split, and inevitably, the balance
> of PV and battery assigned to each distribution panel will not match up
> well at times. A single battery and a single PV system serving the entire
> property is what he really wants. Tesla is not the answer for that today. I
> suggested converting the dual 200A service to a single 400A service and
> using 4-6 Midnite AIOs, but that would get pretty messy.
>
> I do like the idea of having two wall connectors for this purpose. That
> didn't cross my mind. I could possibly convince him to do a GW3/PW3 system
> for one 200A panel and just a Powershare for the other panel (without PV
> recharging). It depends on what is on each panel I suppose. The Powershare
> is only 110A LRA, so it might not start up larger AC units without soft
> start. The whole idea isn't too practical, but he wants to explore all
> options.
>
> Also, as of today, Powershare does not work with the Gateway 3 with
> Powerwall 3. They are working on an OTA firmware update to support this.
> For now, it's just unidirectional charging from the Wall Connector. You
> need the Gateway 3V for Powershare to work, but that does not work with
> Powerwall 3, so it's a waiting game.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Tue, Feb 18, 2025 at 5:12 PM Matt Partymiller <matt at sesre.com> wrote:
>
>> Jason,
>>
>>
>>
>> Sounds like an interesting market.
>>
>>
>>
>> A transfer switch is probably more expensive than two Tesla vehicle
>> chargers, one for each system. He just needs to remember which one to plug
>> into and you just need to sell at least 4 PW3s, a couple gateways and
>> you’re in business….
>>
>>
>>
>> Matt
>>
>>
>>
>>
>>
>>
>>
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
>> Behalf Of *Jason Szumlanski via RE-wrenches
>> *Sent:* Tuesday, February 18, 2025 5:05 PM
>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Cc:* Jason Szumlanski <jason at floridasolardesigngroup.com>
>> *Subject:* Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery
>> backup
>>
>>
>>
>> *Caution:* This email originated from outside SES. Do not click links or
>> open attachments unless you recognize the sender and know the content is
>> safe.
>>
>>
>>
>> Not bragging, but many of my clients in this situation are billionaires
>> or at least some sizable fraction of that. Naples is a pretty interesting
>> place. They are usually not willing to compromise. On the three barrier
>> islands where I do off-grid work, it always starts off as a few mini-splits
>> and then it ends up being a few mini-splits and a 5-ton central. And then
>> they install an electric hot tub unbeknownst to me. And then there are
>> three electric golf carts that show up. And how can you enjoy the beach
>> with 30 of your favorite friends without a large ice maker (on top of the
>> undercabinet unit at the outdoor wetbar)? It never ends.
>>
>>
>>
>> For on-grid homes with common 400A service (dual 200A panels) we focus on
>> backing up one panel while installing enough PV to cover the total annual
>> household usage, which is usually the request we get. They would love to
>> back up both panels, but when confronted with the space requirements and
>> battery capacity limitations imposed by NFPA 855, the conversation usually
>> goes my way. As for the PV portion, we always hear that if they can't cover
>> 100%, they don't see the point in doing it. That's why you end up with
>> giant PV arrays with battery capacities more typical of a modest home.
>>
>>
>>
>> I just spent an hour explaining to a customer with an existing 25kW
>> Enphase system why he can't back up two 200A panels with Tesla Powerwall
>> 3's (without serious drawbacks associated with splitting the PV and
>> battery). He was also under the impression that he could use Powershare
>> from his Cybertruck to back up both 200A panels simultaneously, or at least
>> switch easily between them (I actually toyed with the idea of a transfer
>> switch to accomplish this, but decided to just say no).
>>
>>
>>
>> These clients don't hear NO often. On the other hand, they are usually
>> very smart and ask good questions. Most of them didn't get rich by accident.
>>
>>
>> Jason Szumlanski
>>
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>>
>>
>>
>> On Tue, Feb 18, 2025 at 2:38 PM Dave Angelini Offgrid Solar via
>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Still Jason it seems very crazy! When I do energy for a home in your
>> neck, usually offgrid, we use mini-splits and in a large home
>>
>> like you are referring with the grid, the same thing, use a split for a
>> zone, like the kitchen and save all that wasted battery capacity backing up
>> the whole home. They may be a bit uncomfortable without the grid but they
>> can survive a hurricane outage,
>>
>> or longer.
>>
>>
>>
>> The strategy of not backing up it all does require the people to be
>> reasonable and trainable. Very few central air systems are useable without
>> spending 10's of thousands more. I think none unless the owner has more
>> money than brains. Good for the economy I guess but all that lithium has to
>> go to the dump someday.
>>
>>
>>
>> Seems alot of lithium is going to the dump with all these companies
>> building batteries and then going out of business also.
>>
>>
>>
>> Alot of my calls are for systems that the installer has long gone out of
>> business. The owner is clueless because they never had
>>
>> a clue about their power system. No Bueno for sure! Stay Safe !
>>
>>
>>
>> *Dave Angelini Offgrid Solar*
>>
>> *"we go where powerlines don't"*
>>
>> * <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>*
>>
>> *e-mail offgridsolar at sti.net <offgridsolar at sti.net>*
>>
>> *text 209 813 0060*
>>
>>
>>
>> On 2025-02-18 9:42 am, Jason Szumlanski via RE-wrenches wrote:
>>
>> Haha, we would not have the pool heater on a backup system, but many
>> times people want a partial home backup system with whole home annual grid
>> offset.
>>
>>
>>
>> But for practical purposes around here, full-time residents often just
>> trade pool heating for air conditioning based on season. If you size a
>> backup system for central air conditioning, sometimes it is technically
>> possible to heat the pool off-grid in the winter because the house load is
>> otherwise a fraction of what it is in the summer months. In the winter, we
>> sometimes see batteries full by 9:00 am and a lot of wasted solar energy.
>>
>>
>>
>>
>>
>>
>> Jason Szumlanski
>>
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>>
>> On Tue, Feb 18, 2025 at 11:56 AM Dave Angelini Offgrid Solar via
>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Sure I get how important it is to electrically heat a pool in a power outage. 😉
>>
>> *Dave An,gelini Offgrid Solar*
>>
>> *"we go where powerlines don't"*
>>
>> * <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>*
>>
>> *e-mail offgridsolar at sti.net <offgridsolar at sti.net>*
>>
>> *text 209 813 0060*
>>
>>
>>
>> On 2025-02-18 8:05 am, Jason Szumlanski via RE-wrenches wrote:
>>
>> There are many 4,000 sq ft pool homes in my area with electric pool
>> heating and electric everything else where 25kW would just cover the
>> electric bill. Some larger homes around here can definitely require more.
>> Florida Power & Light allows up to 50kW on 120/240V split phase service,
>> but only if expected production does not exceed an estimated 115% of
>> historical annual usage.
>>
>>
>>
>>
>> Jason Szumlanski
>>
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>>
>> On Mon, Feb 17, 2025 at 12:58 PM Dave Angelini Offgrid Solar via
>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Why is there a need for more than 25KW for residential please? Just
>> curious. In Nevada, 25KW is way into commercial.
>>
>>
>>
>> *Dave Angelini Offgrid Solar*
>>
>> *"we go where powerlines don't"*
>>
>> * <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>*
>>
>> *e-mail offgridsolar at sti.net <offgridsolar at sti.net>*
>>
>> *text 209 813 0060*
>>
>>
>>
>> On 2025-02-17 9:43 am, Tyrone Houck via RE-wrenches wrote:
>>
>> Greetings wrenches,
>>
>> In Pacific Power territory we are coming up against roadblocks with
>> regards to whole house battery backup systems with inverter ratings higher
>> than 25kw. Even when the generation capacity is below the 25kw residential
>> limit, net metering applications are being rejected based on the inverter
>> rating.. The inverter rating in these cases is sized to handle the
>> customer's existing loads and will never export more than the 25kw limit
>> dictated by Oregon PUC. I am drafting a letter to Energy Trust, the state,
>> etc. But am curious if anyone else gas had this problem or come up with a
>> solution. I would appreciate to hear any experiences or similar
>> interactions with PGE or PPL or even how this has worked in other
>> jurisdictions, states, etc. Any input or support is greatly appreciated.
>>
>>
>>
>> Tyrone Houck
>>
>> Oregon Solarworks LLC
>>
>> CCB #204937 LRT #076
>>
>> 541-787-1366
>>
>> tyrone at oregonsolarworks.com
>>
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250218/bb6d0e8d/attachment.htm>
More information about the RE-Wrenches
mailing list