[RE-wrenches] 120-240 Transformer loud vibration and humming.
William Miller
william at millersolar.com
Thu Jan 23 22:46:12 EST 2025
Ear plugs?
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Thu, Jan 23, 2025 at 7:44 PM John Blittersdorf via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> The only thing I could find in the whole system that was not up to snuff
> was incomplete separation of neutrals and grounds in the sub-panel. In
> other words more than one ground to neutral bond. But the fact remains that
> this
> system worked flawlessly for 26 years! I also removed the ground wire
> from the transformer but still no difference. What am I missing?
>
> On Thu, Jan 23, 2025 at 10:35 PM John Blittersdorf <
> john.blittersdorf at gmail.com> wrote:
>
>> Steve, I took my scope meter today and checked wave forms at all
>> points. All were clean sine waves. I checked the breaker connections and
>> all connections back to the inverter and all were tight.
>> Voltage drop when pump kicked on was small and only about 1 volt when
>> running. Amp were 12 on both legs.
>>
>> On Thu, Jan 23, 2025 at 9:48 AM Jay via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Are the amps leg the same?
>>> Jay
>>>
>>> On Jan 22, 2025, at 9:29 PM, Steve Higgins via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>
>>> How do their clocks run? Is the Xfmer quiet down when the generator
>>> runs?
>>>
>>> If you have an O-scope, check the output waveform off the inverter. My
>>> guess is that the output waveform will be deformed, causing extra noise for
>>> the Xfmer. You might be able to see this on the frequency as well. It
>>> should be solid at 60Hz, but if it's drifting or way off the high side,
>>> FETS have probably failed.
>>>
>>> If you pull the top cover off the inverter the and you look at the FET
>>> board, it'll be the fets closest to the Fan on the AC board.
>>>
>>>
>>> <image.png>
>>>
>>> Steve Higgins
>>>
>>>
>>>
>>>
>>> On Wed, Jan 22, 2025 at 7:32 PM John Blittersdorf via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> Christopher,
>>>> Update on the Transformer Humming. Installed a new PSX-240 from Kirk
>>>> and it is LOUDER than the T-240 that I took out.
>>>> I have a call into the well driller to see if they have a record of the
>>>> pump size or other details. When connected
>>>> directly to the grid via transfer switch, still loud noise... same with
>>>> battery only. I did not check the 120VAC 30 amp break
>>>> in the backed up loads sub panel. All other wiring was redone as I
>>>> switched the pump directly to the grid until I received the
>>>> new transformer and back to the inverter again. so all the connections
>>>> were redone except the 120 breaker.
>>>>
>>>> John
>>>>
>>>>
>>>> On Wed, Jan 22, 2025 at 10:30 AM Howie Michaelson via RE-wrenches <
>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>
>>>>> John,
>>>>> If you need a T240 (internal or external), I have a few used ones (and
>>>>> maybe a new one) in storage.
>>>>> Howie
>>>>>
>>>>>
>>>>> On Wed, Jan 22, 2025, 10:14 AM Christopher Warfel via RE-wrenches <
>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>
>>>>>> I could be a loose electrical or mechanical connection. It's been
>>>>>> installed for a while and connections could have loosened up from
>>>>>> expansion and contraction.
>>>>>>
>>>>>> On 1/18/2025 9:06 AM, John Blittersdorf via RE-wrenches wrote:
>>>>>> > Hi Wrenches,
>>>>>> > I have a customer with an SW4024 installed in 2003 with the Trace
>>>>>> > T220 transformer for
>>>>>> > her well pump. Recently it has started making a lot of noise when
>>>>>> the
>>>>>> > well pump comes on.
>>>>>> > I checked the current on the well pump and it seems to be in the
>>>>>> > normal range. I have never had a transformer failure. Could this
>>>>>> be a
>>>>>> > failing transformer?
>>>>>> >
>>>>>> > Also, I have not been able to source a new one (Outback T240). Are
>>>>>> > there other brands
>>>>>> > some of you may have used for a step up transformer?
>>>>>> >
>>>>>> > John Blittersdorf
>>>>>> >
>>>>>> > _______________________________________________
>>>>>> > List sponsored by Redwood Alliance
>>>>>> >
>>>>>> > Pay optional member dues here: http://re-wrenches.org
>>>>>> >
>>>>>> > List Address: RE-wrenches at lists.re-wrenches.org
>>>>>> >
>>>>>> > Change listserver email address & settings:
>>>>>> >
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> >
>>>>>> > There are two list archives for searching. When one doesn't work,
>>>>>> try the other:
>>>>>> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> >
>>>>>> > List rules & etiquette:
>>>>>> > http://www.re-wrenches.org/etiquette.htm
>>>>>> >
>>>>>> > Check out or update participant bios:
>>>>>> > http://www.members.re-wrenches.org
>>>>>> >
>>>>>> --
>>>>>> Christopher Warfel, PE
>>>>>> ENTECH Engineering, Inc.
>>>>>> PO Box 871, Block Island, RI 02807
>>>>>> (401) 447-5773
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>>
>>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250123/d90b2cb4/attachment.htm>
More information about the RE-Wrenches
mailing list