[RE-wrenches] ATS models to bypass GT hybrid inverters for maintenance/faults

Stuart Kriendler stuartkriendler at gmail.com
Fri Jan 17 10:28:41 EST 2025


Many thanks again Mac and Wrenches,

This is now put to bed with confirmation the only listed 200A ATS that will
work without a 12V switching controller that I could find around the $1k
mark is indeed the Kohler RDT series.
(All currently manufactured Generac, Briggs & Stratton and Cummins ATS
options require a controller to talk to the same name brand gene to
switch/transfer, or a Mcgiver move.)

I found a supplier in Florida who gave a slight volume discount and seems
solid.
Here is a link to the product, pricing, specs and manual through them:
https://bnhgenerators.com/product/kohler-200-amp-rdt-ats-rdt-cfnc-0200a-qs7/

And another supplier option with similar pricing, and the 100A version
readily available in case helpful:
https://www.electricgeneratorsdirect.com/Kohler-RDT-CFNC-0200A-QS7/p2202.html

Best to all and thanks again.

Sunniest regards,
Stuart
441 599 2105


On Tue, 14 Jan 2025 at 21:02, Mac Lewis <maclewis1 at gmail.com> wrote:

> Hi Stuart,
>
> The Kohler RDT switch is a much better switch for what you are doing; it
> is a power seeking switch with no accessory device communication needed.
> It is more expensive than the RXT switch because it has its own brain
> board.  A Kohler tech can adjust the delays for you if needed but the
> defaults are good.  We have a few of them out there with no issues.    They
> have them available as service entrance rated/indoor/outdoor etc.
>
> Good Luck!
>
> On Tue, Jan 14, 2025 at 2:55 PM August Goers via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hi Stuart,
>>
>> Got it, now I see you're working with the MidNite AIO. This ATS topic
>> came up not too long ago and I posted that we used to have success with
>> Briggs & Stratton ATS units back when we were installing SMA Sunny Island
>> systems. The Briggs unit does not need a control from an external source,
>> it just switches over automatically (with a few second delay) once utility
>> power is lost. We never had a single problem with these transfer switches.
>>
>> You might check them out:
>> https://www.nationwidegenerators.com/briggs-stratton-071270-200-amp-se-rated-120-240v-1ph-ats/?srsltid=AfmBOorCds2ktOcsHUf3GWmX5ba70K-ynjOcm1iizzIW6X-9OkSVpfHA
>>
>> I know that Briggs went through a bankruptcy a few years ago, but maybe
>> they're still alive and kicking now.
>>
>> August
>>
>>
>> On Tue, Jan 14, 2025 at 1:29 PM Stuart Kriendler <
>> stuartkriendler at gmail.com> wrote:
>>
>>> Much appreciated August,
>>>
>>> Yes, that fancy Enphase System Controller is a nice piece of kit,
>>> overseen a few of those and it is nice they pass through the grid power if
>>> there is an issue, most of the time.
>>> ;-)
>>> I'm in love with the MN AIO, the build quality is impressive and great
>>> value for money, with the CBI breakers and features mentioned earlier etc.
>>> all built in.
>>> Now seen an engineering sample do the business in an rugged off-grid
>>> scenario for a few months and feel confident it will be a great GT hybrid
>>> option, one catch is the need for a 3rd party ATS though.
>>> (Hoping Midnite will make one of their own in time, as well as a wireway
>>> to marry the PowerFlo 16 and AIO, both such nicely built solid equipment).
>>>
>>> Hopefully the Kohler RXT or Generac can work to keep the ATS cost below
>>> $1k!
>>>
>>> Sunniest regards,
>>> Stuart
>>> 441 599 2105
>>>
>>>
>>> On Tue, 14 Jan 2025 at 16:02, August Goers <august at luminalt.com> wrote:
>>>
>>>> Hi Stuart -
>>>>
>>>> Many grid tied PV/ESS manufacturers (Enphase, SolarEdge, Franklin,
>>>> Tesla to name a few) now have a Microgrid Interconnect Device (MID) that
>>>> essentially acts as a smart transfer switch thus eliminating the need for a
>>>> 3rd party automatic transfer switch. What brands equipment are you looking
>>>> at?
>>>>
>>>> Best, August
>>>>
>>>> On Tue, Jan 14, 2025 at 11:10 AM Stuart Kriendler via RE-wrenches <
>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>
>>>>> Good day Wrenches,
>>>>>
>>>>> 2025 looks to be the year for installing more grid tied (GT) battery
>>>>> back up hybrid inverters on new and existing GT PV systems in a whole house
>>>>> backup scenario
>>>>> i.e. Utility - Hybrid Inverter - House Loads
>>>>>
>>>>> With these newer GT hybrids so 'sensitive', any fault on the PV side
>>>>> can cause them to shut down, thus stopping power to the house.
>>>>> To minimise this it seems sensible to add an ATS to the system such
>>>>> that if/when the hybrid faults, the ATS w switch to grid power, bypass the
>>>>> hybrid, and power the house.
>>>>> This could save an emergency truck roll or late night phone call for
>>>>> installers.
>>>>>
>>>>> Anyone have experience on good value-for-money Listed automatic
>>>>> transfer switches that would do the job, 200A, 120/240V?
>>>>>
>>>>> Two name brand options that came up on the less expensive end of the
>>>>> spectrum are:
>>>>> - Generac
>>>>> RXSW200A3 (https://www.generac.com/residential-products/standby-generator-transfer-switches/automatic/rxsw200a3/)
>>>>>
>>>>> - Kohler 200-amp, Service Entrance RXT ATS | RXT-JFNC-200ASEQS4 (
>>>>> https://www.kohler.com/content/dam/kohler-com-NA/Lifestyle/PDF/PDF-g11152.pdf
>>>>> )
>>>>>
>>>>> However, they each say their ATSs must be used with the corresponding
>>>>> generator.
>>>>>
>>>>> I would imagine a simple 'grid sense' functionality would mean that if
>>>>> the hybrid's output was connected to the Grid/Normal lugs and the grid was
>>>>> connected to the Gene/Backup lugs in the ATS it should work.
>>>>> However I don't want to end up with an expensive surprise in a
>>>>> relatively remote location where I operate!
>>>>>
>>>>> Would appreciate any feedback with experience with the above or other
>>>>> ATS models or how people are future proofing for this scenario?
>>>>> To do future maintenance/torque checks etc. in a GT hybrid whole home
>>>>> backup situation, it would be nice to bypass the inverter and keep the
>>>>> house powered for safety and homeowner convenience in general.
>>>>>
>>>>> Thanks and best.
>>>>>
>>>>> Sunniest regards,
>>>>> Stuart
>>>>> 441 599 2105
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250117/812f9dbf/attachment.htm>


More information about the RE-Wrenches mailing list