[RE-wrenches] Generator Overvoltage Troubleshoot
Darryl Thayer
darylsolar1 at gmail.com
Fri Jan 3 15:51:23 EST 2025
Here is my two cents I had a similar over voltage. It was caused by the
generator. It helped to put a load on the generator, I put on a 500 watt
resistance load, it helped but in the end the generator was replaced. Good
luck.
On Fri, Jan 3, 2025, 8:17 AM Jim Gowdy via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi all,
> I need some help with a generator overvoltage troubleshoot. I'm
> working on an outback offgrid system that consists of 2 x Radian GS8048a, 1
> x MATE3S controller, 1 x FM 80 charge controller, 1 x 55kw single phase
> propane AC cummins generator, about 4kw of solar *not sufficient enough to
> keep up with the load, and 24 x 4v Rolls batteries series/paralleled to
> make 48v. The generator was rebuilt and the batteries replaced about a
> year ago and since then, the generator has been faulting due to
> overvoltage. I had help and first found that the MATE needed calibrating
> so that was done, but the generator still was faulting. I found changing
> the AC Input Charging from 30a to 20a seemed to work. I put a power
> monitor on the generator output and found that, with the AC Input Charging
> set at 30a, noticed that there was a voltage spike up to 300+V at about a
> 70a draw. The generator company put a load bank on and verified the
> generator may not be at fault and the problem is after the generator. Has
> anyone encountered a problem like this and have suggestions? I've attached
> a PDF with a timeline of what I've done for troubleshooting so far.
>
> --
> Jim with Gowdy Electric
> Cambria, Ca 93428
> business 805 927 2630
> cell 805 975 5279
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250103/9be4622a/attachment.htm>
More information about the RE-Wrenches
mailing list