Thanks Roy.

I am now wondering if instead of 1 Prostar and 1 DC DC Convert I should move to 2 Prostars, 1 for each load voltage.

Each Prostar would have 2 AGM and 2 PV.

In a way this is more complex, but in another simpler.

For AC charging I would also need 2 chargers, one for each voltage.

Humm.

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Roy Butler via RE-wrenches
Sent: Thursday, December 19, 2024 7:03 AM
To: re-wrenches at lists.re-wrenches.org
Cc: Roy Butler <roy at four-winds-energy.com>
Subject: Re: [RE-wrenches] Telecomm Power Supply - Voltages

Hi Mark,

One thing to be aware of is capacitance inrush current, quite common with DC-DC converters.
If you are running the converters off of the Prostar controller load circuit, the inrush current might
be sufficient to trigger a high current shutdown of the load circuit.

A single low current converter will probably be fine, especially if using the 30 amp Prostar.

If you do decide to use the Tristar and go with a 48 volt configuration, 2 converters will not
be an issue because the Tristar has no load circuit, your loads will be powered off of the battery.

I'll put my installer hat back on here and say that I always prefer the least complex solution.
The 24 volt configuration with the single converter would be that solution and also provide LVD.



Roy Butler

Morningstar Technical Support




On 12/19/2024 9:51 AM, Mark Frye via RE-wrenches wrote:
My equipment has both 12 V and 24 V each at about 60W.

I was planning to run a Prostar at 24V and then use a DC DC converter for the 12 V load.

That looked like 2 x 285 AH AGM and 2x 320 W PV.

Now I have to go to a darker place and may have to double the battery and the PV.

That would mean I could run a Tristar at 48V and have a two DC DC converters, one for the 24V loads and one for the 12V loads.

Somehow it makes sense to me to run the supply side at 48V for lower currents and more battery cells even if it means an additional converter on the load side.

Any thoughts one way or the other?

Thanks,

Mark Frye



_______________________________________________

List sponsored by Redwood Alliance



Pay optional member dues here: http://re-wrenches.org



List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



There are two list archives for searching. When one doesn't work, try the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

http://www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

http://www.members.re-wrenches.org



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241219/6cc73cd9/attachment.htm>


More information about the RE-Wrenches mailing list