[RE-wrenches] More Issues with Parallel Sol-Ark 15K System

Jason Szumlanski jason at floridasolardesigngroup.com
Fri Dec 13 20:32:03 EST 2024


Thank you for this tip. I did look at that today. It appears that all four
units have identical hardware. I closely compared them and the circuit
boards all appear identical.  While one serial number was pretty far away
from the other three, that was not the offending unit, and it appears
identical to the others.

Jason




On Fri, Dec 13, 2024, 7:51 PM Tyrone Houck via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Any further investigation into the hardware differences between the newer
> 15k and the original 15k I mentioned before? That was the only thing that
> fixed the issue for us. We had to insist they replaced it with a newer
> matching inverter. I should have made note of the serial numbers to try to
> narrow down the time frame when they changed the design. The newer design
> has a small circuit board bolted to the bottom of the enclosure that wasn't
> present in the original..
>
>
>
>
> On Sat, Nov 9, 2024, 7:16 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> I wrote in another thread about an off-grid quad Sol-Ark system that was
>> shutting down due to parallel stop when one of the four inverters
>> experienced a DC PV fault, and how that shutdown is far from ideal. The
>> same system is down once again, this time due to an AC fault code.
>>
>> The homeowner started getting repeated F18 and F34 AC overcurrent faults
>> on one of the slave inverters. This, in turn, shut the entire system down
>> due to parallel stop faults (F41). None of the other units had AC
>> overcurrent faults, and the load is nowhere near requiring all four
>> inverters for even the most demanding circumstances. It was designed this
>> way for redundancy, which I am quickly finding out is not Sol-Ark's strong
>> suit.
>>
>> To diagnose the issue remotely, I had the owner turn off all four load
>> breakers, all DC PV input, and the AC microinverter input on the GEN
>> terminals. I had them restart everything (several times). Every time, the
>> same inverter would have repeated AC overcurrent faults, and the others
>> would have parallel system faults. Since there were no loads connected by
>> virtue of the load breakers being open, I suspected this had to be an
>> internal fault.
>>
>> I went to the site, and Sol-Ark Tier 1 tech support had me shut off all
>> inverters and take the suspect inverter out of parallel operation mode. As
>> a standalone master it was able to power up and support the entire house
>> load without issue. Then we reprogrammed it for parallel operation again
>> and turned everything back on. We were unable to stay on the phone long
>> enough to determine if this was successful, but ultimately, the fault
>> returned. I was told to call and ask for Tier 2 next time if it happened
>> again, which I intend to do on Monday. At this point, the issue can only be
>> internal to the unit, and I intend to demand warranty replacement of
>> suspect components or the whole unit.
>>
>> I had to get the system running, so I wanted to take the bad inverter out
>> of the parallel system. I was hoping that simply shutting it down would
>> work. This is the third of 4 inverters in the Modbus chain. When turning it
>> off completely (all AC and DC switches disconnected), the 4th inverter
>> would fault, presumably because the Modbus signal was not being relayed,
>> but inverters #1 and #2 worked fine. However, I wanted #4 to also continue
>> working while taking #3 out of service. So then I turned on the battery
>> disconnect for #3 but left it in the off mode by not pressing the on/off
>> button, thinking that it would allow relay of the Modbus signal from #2 to
>> #4. That allowed the system to work momentarily, but then everything
>> faulted out due to parallel system stop. In other words, I was going to
>> have to physically take #3 out of the Modbus daisy chain to make this work.
>>
>> Of course, I didn't have a long enough Cat5 cable with me, nor a Cat5
>> splice connector. So I had to rig something, which I did successfully to
>> jumper from #2 to #4. But when I turned everything back on, #4 still would
>> not work. I eventually realized that you have to change the Modbus address
>> from 04 to 03 in the settings. Apparently, the addresses need to be
>> sequential for it to work. Once I did this, I was able to get the system up
>> and running again as a triple-inverter parallel setup. No faults were
>> observed. So the theory was proven that #3 has an issue internally.
>>
>>
>> Anyway, bottom line, I am disappointed at how one inverter fault takes
>> down the whole paralleled system, and also how taking a faulted inverter
>> out of the system requires physical and programming changes. Turning it off
>> should be sufficient. This is a very poor way to implement a parallel
>> system that should provide the peace of mind that redundancy implies. Now I
>> have a customer who thought they were getting a system with failsafe
>> redundancy that actually requires a service call every time one of the
>> paralleled units decides it does not want to play nicely with others.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241213/b15883a9/attachment.htm>


More information about the RE-Wrenches mailing list