Just a follow-up to this saga... After many many more hours of diagnostics
with tech support, often repeated on subsequent calls, I finally had to get
irritated enough to demand that they just swap out the inverter. On three
different calls they made me take the inverter out of parallel mode and run
it standalone to see if it works, and it did. But when put back in
parallel, it would fault out again. Today they made me put the subject
inverter as the master in parallel mode, and it worked. Then I switched it
back to its original slave position and it faulted out again. They had the
audacity to tell me that some inverters are just like that and I should use
it as the master. Obviously that is a ridiculous resolution to the problem.
I demanded that they fix their faulty product under warranty and they are
now sending me a replacement board and screen. I have a pretty good degree
of confidence that it will fix the problem, but it really should not have
been this hard to get to this point.
The troubleshooting process is broken at Sol-Ark. There is no continuum of
severity that gets issues properly escalated and resolved. Repeated
diagnostic measures just frustrate people and do not solve the issue. You
have to get upset, and even nasty to speak to a supervisor. Meanwhile, the
tier 1 agents are playing a game of telephone, relaying what the higher-ups
are telling them to say. Some of them are knowledgeable, but many are just
parroting what someone else to whispering in their ear, even when they
don't have the full picture. It's like throwing spaghetti at a wall to see
what sticks.
I will report back when I get the replacement parts and try them out.
Jason Szumlanski
Florida Solar Design Group
On Sat, Nov 9, 2024, 10:15 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> I wrote in another thread about an off-grid quad Sol-Ark system that was
> shutting down due to parallel stop when one of the four inverters
> experienced a DC PV fault, and how that shutdown is far from ideal. The
> same system is down once again, this time due to an AC fault code.
>
> The homeowner started getting repeated F18 and F34 AC overcurrent faults
> on one of the slave inverters. This, in turn, shut the entire system down
> due to parallel stop faults (F41). None of the other units had AC
> overcurrent faults, and the load is nowhere near requiring all four
> inverters for even the most demanding circumstances. It was designed this
> way for redundancy, which I am quickly finding out is not Sol-Ark's strong
> suit.
>
> To diagnose the issue remotely, I had the owner turn off all four load
> breakers, all DC PV input, and the AC microinverter input on the GEN
> terminals. I had them restart everything (several times). Every time, the
> same inverter would have repeated AC overcurrent faults, and the others
> would have parallel system faults. Since there were no loads connected by
> virtue of the load breakers being open, I suspected this had to be an
> internal fault.
>
> I went to the site, and Sol-Ark Tier 1 tech support had me shut off all
> inverters and take the suspect inverter out of parallel operation mode. As
> a standalone master it was able to power up and support the entire house
> load without issue. Then we reprogrammed it for parallel operation again
> and turned everything back on. We were unable to stay on the phone long
> enough to determine if this was successful, but ultimately, the fault
> returned. I was told to call and ask for Tier 2 next time if it happened
> again, which I intend to do on Monday. At this point, the issue can only be
> internal to the unit, and I intend to demand warranty replacement of
> suspect components or the whole unit.
>
> I had to get the system running, so I wanted to take the bad inverter out
> of the parallel system. I was hoping that simply shutting it down would
> work. This is the third of 4 inverters in the Modbus chain. When turning it
> off completely (all AC and DC switches disconnected), the 4th inverter
> would fault, presumably because the Modbus signal was not being relayed,
> but inverters #1 and #2 worked fine. However, I wanted #4 to also continue
> working while taking #3 out of service. So then I turned on the battery
> disconnect for #3 but left it in the off mode by not pressing the on/off
> button, thinking that it would allow relay of the Modbus signal from #2 to
> #4. That allowed the system to work momentarily, but then everything
> faulted out due to parallel system stop. In other words, I was going to
> have to physically take #3 out of the Modbus daisy chain to make this work.
>
> Of course, I didn't have a long enough Cat5 cable with me, nor a Cat5
> splice connector. So I had to rig something, which I did successfully to
> jumper from #2 to #4. But when I turned everything back on, #4 still would
> not work. I eventually realized that you have to change the Modbus address
> from 04 to 03 in the settings. Apparently, the addresses need to be
> sequential for it to work. Once I did this, I was able to get the system up
> and running again as a triple-inverter parallel setup. No faults were
> observed. So the theory was proven that #3 has an issue internally.
>
>
> Anyway, bottom line, I am disappointed at how one inverter fault takes
> down the whole paralleled system, and also how taking a faulted inverter
> out of the system requires physical and programming changes. Turning it off
> should be sufficient. This is a very poor way to implement a parallel
> system that should provide the peace of mind that redundancy implies. Now I
> have a customer who thought they were getting a system with failsafe
> redundancy that actually requires a service call every time one of the
> paralleled units decides it does not want to play nicely with others.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241213/331dbed3/attachment.htm>
More information about the RE-Wrenches
mailing list