[RE-wrenches] SunPower SunVault black start
Kevin Pegg
kpegg at energyalternatives.ca
Wed Dec 11 14:24:09 EST 2024
Hi Bruce,
I just had a similar situation, different batteries, and used the Iota DLS 48 / 13 charger. Connected it directly to the cells bypassing the BMS, as it had opened the contactors to the regular power terminals. Took about 1hr of charge for the BMS to power up. I didn’t worry about any specific lithium settings or trying to close loop it, just used it as a jump start. We had other issues with the batteries that ended up being comms problems from being improperly configured preventing contactors from engaging. If it wasn’t for that, I expect would have been able to power up the inverter and resume normal charging within 1hr.
Kevin
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Bruce Erickson via RE-wrenches
Sent: December-11-24 11:09 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Bruce Erickson <bruce at mendocinosolar.com>
Subject: [RE-wrenches] SunPower SunVault black start
Recently one of our four now-orphaned SunVault systems failed to back up for our customer. On site we found the batteries discharged below cut-in voltage for unknown reasons (no more monitoring, no more tech support). Even though it had been sunny for a few days the system failed to retain a reserve to restart once sun returned. I’m looking for recommendations for 48 volt external chargers for this situation. We’re looking at Iota which only has a 13 amp charger at 48v but does have a plug-in module for controlling LiFePo charging. At 256 amphours of parallel batteries hopefully an 8 or 10 hour charge would get us up to cut-in. I’m also not sure how the Iota will play with any BMS the SunPower batteries might have. Any recommendations for this situation would be much appreciated.
Thanks in advance,
Bruce
Bruce Erickson
Mendocino Solar Service
707-937-1701
PO Box 1252
Mendocino, CA 95460
[cid:image001.jpg at 01DB4BBF.31FD4440]
"Serving the Solar System"
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241211/e1c5fe7d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5686 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241211/e1c5fe7d/attachment.jpg>
More information about the RE-Wrenches
mailing list