I had one stuck in silent a couple years ago. Was plain as day after some
measurements that PV positive to ground showed the open circuit PV voltage.
It had failed internally. A new charge controller fixed it.
*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
*Owner|Principal, VT Solar, LLC*
*Celebrating our 33st Anniversary 1991-2024!!*
dba Vermont Solar Engineering
802.559.1225
On Wed, Dec 11, 2024 at 2:13 PM Luke Christy via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> This is a timely thread. Thanks to all for your input.
>
> I also have a site with a problematic FM100. The system has 2x FM100s and
> every morning one of them has required a manual power cycle by the client
> to get it to start producing. I can get no data remotely through Optics
> that indicates what’s going on other than that the device just stays in
> silent mode after it shuts down at the end of the production day. I went
> down some rabbit holes related to installing a fixed resistor on the BTS
> sensor circuit to set the measured battery temp at 25º C vs leaving the
> sensor unconnected with the lithium battery bank. There were some threads
> on the NAWS forum that indicated ghost temp values from unconnected BTS
> sensors might a source of the problem. I’m not sure why I didn’t think of
> the AFCI card as possible cause also. Thankfully I have some spare new
> FM100s on hand. Looks like a trip out there to swap the device and pull
> some AFCI cards.
>
> I continue to be dismayed at the situation with Outback. I can’t really
> see them coming back to the market in an incarnation that we will
> recognize. - despite the various reports to the contrary. I hope I’m wrong.
> At least (for now) they are still supporting the Optics platform.
>
> Luke Christy
> Renewable energy consultant
>
> NABCEP Certified PV Installation Professional™:
>
> Solar Gain Services, LLC
> PO Box 531
> Monte Vista, CO 81144
> 719.588.3044
> sgsrenewables at gmail.com
>
> On Dec 10, 2024, at 8:50 PM, John Blittersdorf via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> HI Wrenches,
> I have an off grid site on an Island on auto pilot for the winter with
> no access. The FM 100
> has remained in Silent mode even when the Array Voltage is around 150
> Volts and battery at 46V
> I did get a response from Outback Tech support but they couldn't figure
> out what happened.
> I suspect that there is a ground or arc fault error which locks it up til
> manually recycled. The problem is that there is no indication found on
> Optics that there is a ground fault.
> We would be totally in the dark except the original small solar array with
> an Apollo CC with
> about a kilowatt of solar has been dribbling in enough power to keep above
> low battery cutoff
> for a few hours each day. The system was up when I was on the tech
> support call but has since quit for the day. Has anyone seen this before?
>
> John Blittersdorf
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241211/fb6abc65/attachment.htm>
More information about the RE-Wrenches
mailing list