[RE-wrenches] More Issues with Parallel Sol-Ark 15K System
Christopher Warfel
cwarfel at entech-engineering.com
Thu Nov 14 09:37:48 EST 2024
Can you point to a reference to what stage 0 is? This is a new term for
me. So far, have not installed multiple Sol-Ark inverters at one site.
Thank you, Chris
On 11/12/2024 12:50 PM, Poole, Jharen via RE-wrenches wrote:
> Our inverters utilize CANbus communications for establishing parallel
> operation between multiple Sol-Ark inverters. CANbus communication
> operates as a serial communication protocol. In this setup each
> inverter in the setup is linked via a parallel communication cable
> forming a daisy-chain configuration. If one inverter in the chain
> experiences a shutdown due to a fault, the communication chain is
> disrupted. Consequently, the other inverters will also power down when
> we see this loss, ensuring system protection and safeguarding the
> customer’s investment.
>
> Paralleling must be done at a stage 0 they have to sync and that is
> done in the pre normal mode, functionality wise having them going into
> sync is extremely difficult due to timing issues. It's easier to time
> it from a stage 0 than to do it when one unit is already running.
>
> Maintaining synchronization between inverters is critical; if the
> inverters were to operate out of parallel it can result in conflicts
> between the operation of inverters and desynchronization of the units.
> This misalignment can escalate, potentially causing significant damage
> to one or more inverters and risking harm to other connected equipment.
>
>
> Best Regards,
>
> Jharen Poole
> Applications Engineer II
> 972-575-8875
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel, PE
Entech Engineering, Inc.
POB 871 Block Island, RI 02807
401-447-5773
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241114/61c84a41/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-glvzpbsr.png
Type: image/png
Size: 82002 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241114/61c84a41/attachment.png>
More information about the RE-Wrenches