[RE-wrenches] More Issues with Parallel Sol-Ark 15K System

James Jarvis jj at aprsworld.com
Sun Nov 10 12:22:59 EST 2024


There isn't. It's a cultural thing. All of our Japanese machines have
completely different grounding schemes that they want because that is
standard in Japan. That's my two cents

thank you,

-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727

(apologies for the brevity and spelling...from my phone)

On Sun, Nov 10, 2024, 11:02 AM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Can someone/s offer up any solid electrical engineering reason for that?
>
> Makes no sense to me.
>
> Jay
>
> On Nov 10, 2024, at 9:12 AM, david quattro via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> 
> SolArk tech support told us that the PV array ground shouldn’t land on the
> inverter ground bar. But instead should be run to its own local electrode.
>  or if you're grid tied it can land on the ground bar at the Main AC
>
>
>
> On Sun, Nov 10, 2024 at 6:27 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> This is very valuable information. The homeowner sourced these four
>> inverters from someone else before I got involved. Three of the four
>> inverters have a Savant sticker on the front of them. The one without the
>> Savant sticker is NOT the one that is having the problem, but it is
>> adjacent to it. The stickerless inverter is #2 (first slave), but the
>> problem inverter is #3 (second slave). I am assuming the three with the
>> stickers are the same (#1, #3, and #4), but perhaps the one without the
>> sticker has different hardware. I will do a visual inspection the next time
>> I am out there.
>>
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Sat, Nov 9, 2024 at 4:33 PM Tyrone Houck via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> We've noticed a compatability issue with the limitless 15k units and the
>>> newest incarnation of the same(limitless 15k) inverter(additional circuitry
>>> in the wiring compartment associated with the pv inputs is the one way I'm
>>> aware of to tell the difference)..the older units and the newer units don't
>>> seem to play nice with each other though they work fine independently. The
>>> problem we had was one was throwing an arc fault error and the other
>>> parallel faulting in response. The ultimate fix was replacing the older one
>>> with a newer one to match. Not sure if that's what is happening at your
>>> site but after extensive troubleshooting our conclusion was one inverter
>>> was sensing something in the other inverter. May be worth checking to see
>>> if they are all the exact same hardware.
>>> Good luck.
>>>
>>> On Sat, Nov 9, 2024, 8:46 AM Jason Szumlanski via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> I agree with that diagnosis. I did a visual inspection of the boards
>>>> and ribbon cables, and everything seems to be okay. It's strange that the
>>>> inverter worked fine in standalone mode. That points to something in the
>>>> paralleling circuitry or software. Getting past Tier 1 tech support can be
>>>> agonizing, but at least I have an established case now. As a customer
>>>> service gesture, I'm prepared to take a new unit off my shelf and fight
>>>> with Sol-Ark later to get this system back up and running as the quad setup
>>>> that my customer purchased. This should have been a clear cut RMA by Tier 1
>>>> support in my opinion.
>>>>
>>>> Jason Szumlanski
>>>> Principal Solar Designer | Florida Solar Design Group
>>>> NABCEP Certified Solar Professional (PVIP)
>>>> Florida State Certified Solar Contractor CVC56956
>>>> Florida Certified Electrical Contractor EC13013208
>>>>
>>>>
>>>> On Sat, Nov 9, 2024 at 11:33 AM Jerry Shafer <jerrysgarage01 at gmail.com>
>>>> wrote:
>>>>
>>>>> Jason,
>>>>> Everything points to a internal issue maybe with a CT, ribbon
>>>>> connection or just a bad board, regardless a new inverter is the key and
>>>>> solark should really want to investigate the issue themselves anyway.
>>>>> Fun times
>>>>>
>>>>> On Sat, Nov 9, 2024, 7:16 AM Jason Szumlanski via RE-wrenches <
>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>
>>>>>> I wrote in another thread about an off-grid quad Sol-Ark system that
>>>>>> was shutting down due to parallel stop when one of the four inverters
>>>>>> experienced a DC PV fault, and how that shutdown is far from ideal. The
>>>>>> same system is down once again, this time due to an AC fault code.
>>>>>>
>>>>>> The homeowner started getting repeated F18 and F34 AC overcurrent
>>>>>> faults on one of the slave inverters. This, in turn, shut the entire system
>>>>>> down due to parallel stop faults (F41). None of the other units had AC
>>>>>> overcurrent faults, and the load is nowhere near requiring all four
>>>>>> inverters for even the most demanding circumstances. It was designed this
>>>>>> way for redundancy, which I am quickly finding out is not Sol-Ark's strong
>>>>>> suit.
>>>>>>
>>>>>> To diagnose the issue remotely, I had the owner turn off all four
>>>>>> load breakers, all DC PV input, and the AC microinverter input on the GEN
>>>>>> terminals. I had them restart everything (several times). Every time, the
>>>>>> same inverter would have repeated AC overcurrent faults, and the others
>>>>>> would have parallel system faults. Since there were no loads connected by
>>>>>> virtue of the load breakers being open, I suspected this had to be an
>>>>>> internal fault.
>>>>>>
>>>>>> I went to the site, and Sol-Ark Tier 1 tech support had me shut off
>>>>>> all inverters and take the suspect inverter out of parallel operation mode.
>>>>>> As a standalone master it was able to power up and support the entire house
>>>>>> load without issue. Then we reprogrammed it for parallel operation again
>>>>>> and turned everything back on. We were unable to stay on the phone long
>>>>>> enough to determine if this was successful, but ultimately, the fault
>>>>>> returned. I was told to call and ask for Tier 2 next time if it happened
>>>>>> again, which I intend to do on Monday. At this point, the issue can only be
>>>>>> internal to the unit, and I intend to demand warranty replacement of
>>>>>> suspect components or the whole unit.
>>>>>>
>>>>>> I had to get the system running, so I wanted to take the bad inverter
>>>>>> out of the parallel system. I was hoping that simply shutting it down would
>>>>>> work. This is the third of 4 inverters in the Modbus chain. When turning it
>>>>>> off completely (all AC and DC switches disconnected), the 4th inverter
>>>>>> would fault, presumably because the Modbus signal was not being relayed,
>>>>>> but inverters #1 and #2 worked fine. However, I wanted #4 to also continue
>>>>>> working while taking #3 out of service. So then I turned on the battery
>>>>>> disconnect for #3 but left it in the off mode by not pressing the on/off
>>>>>> button, thinking that it would allow relay of the Modbus signal from #2 to
>>>>>> #4. That allowed the system to work momentarily, but then everything
>>>>>> faulted out due to parallel system stop. In other words, I was going to
>>>>>> have to physically take #3 out of the Modbus daisy chain to make this work.
>>>>>>
>>>>>> Of course, I didn't have a long enough Cat5 cable with me, nor a Cat5
>>>>>> splice connector. So I had to rig something, which I did successfully to
>>>>>> jumper from #2 to #4. But when I turned everything back on, #4 still would
>>>>>> not work. I eventually realized that you have to change the Modbus address
>>>>>> from 04 to 03 in the settings. Apparently, the addresses need to be
>>>>>> sequential for it to work. Once I did this, I was able to get the system up
>>>>>> and running again as a triple-inverter parallel setup. No faults were
>>>>>> observed. So the theory was proven that #3 has an issue internally.
>>>>>>
>>>>>>
>>>>>> Anyway, bottom line, I am disappointed at how one inverter fault
>>>>>> takes down the whole paralleled system, and also how taking a faulted
>>>>>> inverter out of the system requires physical and programming changes.
>>>>>> Turning it off should be sufficient. This is a very poor way to implement a
>>>>>> parallel system that should provide the peace of mind that redundancy
>>>>>> implies. Now I have a customer who thought they were getting a system with
>>>>>> failsafe redundancy that actually requires a service call every time one of
>>>>>> the paralleled units decides it does not want to play nicely with others.
>>>>>>
>>>>>> Jason Szumlanski
>>>>>> Florida Solar Design Group
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>>
>>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241110/d8a5f297/attachment.htm>


More information about the RE-Wrenches mailing list