[RE-wrenches] Midnite Powerflo16 with Radian

Tyrone Houck tyronehouck at gmail.com
Sat Nov 9 16:28:30 EST 2024


Maybe a silly question but have you tried shutting off all load breakers(ac
output) and charge controller breakers before powering up? I've noticed
radians have a hard time powering up on homegrids if they have a load. If I
have to do a hard reset on a radian I also shutdown the charge controllers
and turn on inverter battery breaker first followed by charge controller
breakers and finally ac output breaker. Otherwise it does a thing where the
radian fan comes on and off rapidly like it's trying to turn on but doesnt.
I've had it also throw an error on FM100s. Not sure if this is related but
it seemed like it may be relevant. Best of luck.

Tyrone Houck
Oregon Solarworks LLC
LRT #076
541-787-1366
tyrone at oregonsolarworks.com






On Sat, Nov 9, 2024, 12:40 PM Nick Lucchese via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Greetings Wrenches,
>
> Wondering if any of you have successfully paired the new Powerflo16 with a
> GS8048-A yet? There is no reason it shouldn't work yet I've unsuccessfully
> been to a customer's site three times now without a fix. The Radian setup
> had been in use with an FLA Trojan pack for years till their demise due to
> the client unknowingly turned off the AC input source to keep them charged
> for his backup system lacking PV. Network is too far away therefore I
> didn't have Optics otherwise I would have caught it. Have not ruled out
> that there may have been another fault with the Radian before all this but
> the AC input seemed most logical and was known to be turned off by accident
> previously.
>
> Upon closing the Powerflo battery breaker to inverter the Mate3s lights up
> momentarily while briefly receiving full voltage but then DC voltage sinks
> to around 2-18vdc then either trips the breaker on the Powerflo16 or lights
> up the fault indicator. Spoke with Midnite support and they recommended a
> workaround to the BMS pre-charge boot up process but that didn't resolve
> the issue either. I originally thought it must be a failed Spare215 power
> supply board but after swapping there was no effect. Next return trip I
> brought a Rosie with me and everything powered up just fine so I then
> figured it would be the Spare 204 board stack but had the same exact effect
> when I tried that swap today. My next step is returning to swap the
> Spare-205 power control modules but first I'm going to unbox another
> Powerflo16 at my shop and pair it with a brand new Radian that has not yet
> been cannibalized. I've installed 42 Radians and only had two with failed
> Spare-205 control modules but each time it was a similar outcome with them
> being the last thing I swapped to success.
>
> I'm thinking it must be a failed Spare-205 but since the Powerflo has only
> been shipping for a couple months I just wanted to run this by the group to
> see how many have successfully paired these two components at this point.
> The Radian is still under warranty but that seems pretty meaningless at
> this point. One way or another this job is going to be a loss at this point
> but oddly still having fun working through a new head scratcher.
>
> Thanks for any insight, Nick
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241109/e3515840/attachment.htm>


More information about the RE-Wrenches mailing list