[RE-wrenches] Fronius Symo 10.0-3 208V 3 phase WYE without neutral
James Jarvis
jj at aprsworld.com
Tue Nov 5 09:47:21 EST 2024
Hi Group,
We have an install with four Fronius Symo 10.0-3 inverters connected to a
208V WYE building hundreds of feet away. While the building has a neutral,
I would like to avoid sending the neutral out to the inverters as it is a
waste of materials. More wire, bigger conduit, neutral kits in disconnects,
etc.
The Symo manual indicates that there is a wye grid configuration with three
phase and a neutral. And there is a delta configuration with three phase
only. Both appear as though they can be set to 208V
[image: image.png]
I can't see any reason why I can't program the inverters at Delta and not
have a neutral. Am I missing anything? I tried inquiring with Fronius, but
it's a process and the conduit has to go into the ground today.
Thanks wrenches!
-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241105/fed302b5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 112905 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241105/fed302b5/attachment.png>
More information about the RE-Wrenches
mailing list