Dave – w.r.t #3, I think this is mostly a requirement from the inverter manufacturer.

For SMA, there is a minimum DC voltage required in shutdown (when there is also no AC voltage).  This minimum can come from one string, that is, only the longest string needs to be over the minimum, the others can be shorter.

For the SBSE -US, Section 7.6 “Rapid Shutdown Equipment) (pg 28-29) of the System Manual contains this minimum (3.6 Vdc) along with other system requirements. So for the APsmart devices, this would be 6 or more devices required on one string, from the 0.6V minimum shutdown voltage APsmart states.

System manual link: https://files.sma.de/downloads/Home-Storage-Solution-BackupStart-US-SH-en-10.pdf

Please note SMA  commercial inverters may have a larger minimum standby voltage requirement, thought very short strings are not as common as in residential.

Best regards –
Mike

Michael Mahon (he/him)
Solar Academy Manager  |  SMA America
3925 Atherton Rd
Rocklin, CA 95765
+1 916 918 9412
SMA America website<https://www.sma-america.com/>
Solar Academy website<https://solaracademy.sma.de/en/>
US English TechTip<https://www.youtube.com/playlist?list=PLoiOll7F4i-_Wc4JVN8ga2x2vxc8xews_> channel
Upcoming SMA America trainings: English<https://solaracademy.sma.de/en/courses.html?filter%5b1%5d=English&filter%5b2%5d=United%20States>

[cid:image001.jpg at 01DB2B75.AB5BA6C0]<https://www.sma-america.com/products/hybrid-inverters/sunny-boy-smart-energy>
This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Brian Mehalic via RE-wrenches
Sent: Thursday, October 31, 2024 8:03 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Brian Mehalic <brian at solarenergy.org>
Subject: Re: [RE-wrenches] APS rapid shutdown

Not sure about #2 or #3, but 100% yes on #1, which quite a few people (including the mfg?) “learned the hard way.”
Brian


On Oct 31, 2024, at 6:57 AM, Dave Tedeyan via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:

Hi All,

I am about to use the AP systems rapid shutdown units for the first time (pairing with SMA inverters). I was reading through the manual and came across a couple things that I am wondering if others have noticed issues with:

1. The manual states that you need to keep the PV conductors from each inverter (there are two in this system) separate, or else there may be crosstalk. So this would imply that you need to have two separate DC conduits from the roof to the inverters, rather than one. Has anyone noticed if this is truly a concern?

2. The manual also states that there needs to be at least 20cm (or ~8") from the RSD-S-PLC to another piece of equipment (other than the module it is mounted on). I am attaching a diagram from the manual, but it sounds like if you have three rows of modules, the RSD's need to be installed on the top of the top row, the bottom of the bottom row, and you need an 8" gap between the rows for the middle row. The diagram in the manual makes this more clear than my words can. But has anyone not installed this large gap and had issues, or did it still work just fine?

3. Lastly, I don't see a mention in the manual, but is there a string length minimum? For some reason I thought with some of the older Tigo RSD units you needed at least 5 or 6 in a string, or maybe I am thinking of SolarEdge optimizers. I just want to make sure there is no minimum, since another job coming up will have a string of 3 panels.

I appreciate your experience!
Cheers,
Dave

--

[Logo]<https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com<http://www.sungineersolar.com/>
c: (607) 270-0370
<aps rsd.pdf>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241031/338a44e9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 22040 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241031/338a44e9/attachment.jpg>


More information about the RE-Wrenches mailing list