[RE-wrenches] New Outback FXR Series as GTGBB on existing Off Grid Home

Ray Walters ray at solarray.com
Fri Oct 25 13:57:17 EDT 2024


I dealt with this on my "last" GTBB system.  I say last, because I only 
do backup systems now in places like Puerto Rico that actually need 
backup.  The FXRs will NOT connect to even an inverter generator (Yamaha 
EF3000), unless they are programmed to GEN.  Our solution was to save 
two different system profiles on the Mate, and the customer, after 
actuating the transfer switch was to switch to the other profile on the 
Mate.  Power reliability before GTBB:  99.9%,  Power Reliability after 
GTBB was installed: 80%.

The FXRs had firmware problems that caused one inverter (and half the 
backup loads) to shut off when trying to sell back. Outback Tech support 
blamed me for the problems, and only after several months of shut downs, 
did they acknowledge that their firmware was actually the issue.  
Customer spent $30k+ for less reliability.

Magnum going away?  Probably a good thing too, since I had my first out 
of the box failure this Spring, after an almost perfect record over the 
past 15 years.  Customer was on generator power for over 2 months 
waiting for the replacement.  My whole career has been marked with great 
companies being sold, only to see them later drown in a cesspool of 
mediocre products and poor tech support.

Ray Walters
Remote Solar

On 10/24/2024 5:55 PM, Bradley Bassett via RE-wrenches wrote:
> As I remember the FXR inverters will rarely connect to any generators 
> beside very well controlled or inverter type generators. I agree that 
> I don't think there is any automatic transfer from grid tie to 
> generator input.
>
> Brad Bassett
>
> On Thu, Oct 24, 2024 at 3:42 PM Wayne Irwin via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
>
>     It is my understanding that the FXR will not "automatically"
>     switch from Grid Input to Gen.
>     To my knowledge this is a manual option only.
>     I do not recall any way to make this happen automatically. That
>     would have been great.
>
>     You can however still call for the generator at a low V setting
>     and have the generator power an external charger to boost the
>     batteries.
>     I think the brand we used to use was IOTA however, I have also
>     seen golf cart chargers used.
>
>
>     Wayne Irwin
>     President
>     License #CVC56695
>     State Licensed Solar Contractor
>     Pure Energy Solar International Inc.
>     Wayne at PureEnergySolar.com
>     PureEnergySolar.com <http://pureenergysolar.com/>
>     SolarChargingStation.com <http://solarchargingstation.com/>
>     352 377-6527 Office
>     352 336-3299 Fax
>
>
>     The Sun Is Always Shining!
>
>     The content of this message is Pure Energy Solar Confidential. If
>     you are not the intended recipient and have received this message
>     in error, any use or distribution is prohibited. Please notify me
>     immediately by reply e-mail and delete this message from your
>     computer system. Thank you.
>
>     ------------------------------------------------------------------------
>     *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>     behalf of Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org>
>     *Sent:* Thursday, October 24, 2024 5:57 PM
>     *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>     *Cc:* Jay <jay.peltz at gmail.com>
>     *Subject:* Re: [RE-wrenches] New Outback FXR Series as GTGBB on
>     existing Off Grid Home
>     Hi Jeremy
>
>     There are two issues I think.
>
>     1 is that the inverter won’t connect.
>     And I don’t have an answer why the inverter won’t in sell mode but
>     will in gen mode. Maybe the generator is slightly out of the more
>     narrow window for grid. I presume you’ve checked hz and volts and
>     they are in spec for grid?  I know sometimes the frequency control
>     can be slightly variable without a load. I’ve had success in the
>     past getting inverters to connect to a generator with putting some
>     dumb loads on it. Like incandescent lights or small heater.
>
>     2. Maybe it’s a good thing it won’t because if it did connect
>     wouldn’t it be possible for the inverter to try to sell to the
>     generator?  If you didn’t have to change grid to Gen?
>
>     Jay
>
>>     On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches
>>     <re-wrenches at lists.re-wrenches.org> wrote:
>>
>>     
>>     Wrenches,
>>     We have a client that has brought utility power in and we now
>>     have the system hooked up to the utility.
>>     In setting the system up, I've experienced that the inverter will
>>     sell and function fine with all the settings set up as* Grid
>>     Tied* mode, but it does not play nice when the grid is gone , and
>>     the Generator is brought in as the AC source.
>>     We have installed an external transfer switch to switch the
>>     inverters' AC input, from either the utility or the existing
>>     backup generator ( if the grid fails), automatically.
>>
>>     The manual states that the inverter's two input selections can be
>>     programmed for seperate input modes, via the* Input* *Type* menu.
>>     Ive not been able to get this accomplished.
>>
>>     When simulating a grid outage, thus changing the AC input to the
>>     inverter being from the Generator, the inverter will not synch to
>>     the AC power to charge the batteries.
>>     The only way that I can get the inverter to synch, is to switch
>>     the input mode to *GEN* from *GRID.*
>>     This is not ideal since the client would need to be present to
>>     make the button push, even though the generator will be started
>>     automatically if the grid were to go down (hopefully) , just as
>>     it did before.
>>     With no way to contact Outback , can someone advise how to
>>     properly program the inverter/ MATE3S for this project?
>>     Equipment onsite:
>>     Single VFXR3648 inverter
>>     Two FM60 CCs
>>     Hub4
>>     MATE3S
>>     ATS with Dual Relays 50A
>>     L.A. Battery bank
>>
>>     Here's how we would like it to work:
>>     Utility power ON:
>>     Sell excess power once the batteries have gone through the Absorb
>>     cycle. Batteries remain full in case of a utility failure.
>>     Utility Outage:
>>     ATS now feeds Inv AC input via Generator if needed.
>>     Inverter runs the home as it did , off grid.
>>     If the battery voltage drops and the AGS is engaged, the inverter
>>     will use that input to charge the batteries as usual.  If the
>>     grid comes back on and the gen is running, the generator can
>>     still run, with no connection to the inverter. With the grid now
>>     charging the battery bank, and the AGS will enventually shut off
>>     the Gen. Based on voltage.
>>     Contact me off list if necessary
>>
>>
>>     Jeremy Rodriguez
>>     All Solar Inc.
>>     Penrose, CO
>>     719-276-4954
>>
>>
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     Pay optional member dues here: http://re-wrenches.org
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     There are two list archives for searching. When one doesn't work,
>>     try the other:
>>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>     List rules & etiquette:
>>     http://www.re-wrenches.org/etiquette.htm
>>
>>     Check out or update participant bios:
>>     http://www.members.re-wrenches.org
>>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     Pay optional member dues here: http://re-wrenches.org
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     There are two list archives for searching. When one doesn't work,
>     try the other:
>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     http://www.re-wrenches.org/etiquette.htm
>
>     Check out or update participant bios:
>     http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241025/ec0cef1a/attachment.htm>


More information about the RE-Wrenches mailing list