Rick:
If I had to guess I’d say you have a PV wiring fault. The PV positive may
be shorted to ground.
This would make the inverter chassis negative in relation to ground.
The logic I use is to ask what is the likely source of DC at 195 volts? It
is most likely the PV circuits, wouldn’t you say?
If the DC Fault is not eternal then it must be internal to the inverter.
This could be a dangerous situation. I would proceed with caution.
Try completely isolating the PV from the inverter as a start.
Good luck.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *rick--- via RE-wrenches
*Sent:* Tuesday, October 15, 2024 11:09 AM
*To:* RE-wrenches
*Cc:* rick at solshineenergy.com
*Subject:* [RE-wrenches] Sol-Ark Gen Input
Back on the Sol-Ark topic again. We have a customer whose 12kW is measuring
-195VDC to ground from L1 and L2 with the Gen breaker open. L1 to L2 = 0V.
I know the Gen input can be configured as an output, but reading a high DC
voltage to ground is concerning. The generator has never been run. System
is operating normally.
Anyone have a Sol-Ark accessible that could verify what they’re reading?
Thanks in advance.
Rick Brown
Solshine Energy
Solar Electric Contracting Services
www.solshineenergy.com
Roanoke, VA
Office: 540.235.3095
Mobile: 540.808.9502
CONFIDENTIALITY NOTICE -- This email is intended only for the person(s)
named in
the message header. Unless otherwise indicated, it contains information
that is
confidential, privileged and/or exempt from disclosure under applicable
law. If you have
received this message in error, please notify the sender of the error and
delete the
message. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241015/579d9b00/attachment.htm>
More information about the RE-Wrenches
mailing list