[RE-wrenches] Enphase Batteries and IQ7+ Won't Restart
jay
jay.peltz at gmail.com
Mon Sep 30 20:04:05 EDT 2024
Thx Wayne.
Curious, I guess they are in a sense AC batteries, as there is no way to access them for DC jump charge?
And I guess that is the same with Tesla? In that there is not way to access the battery, or they didn’t figure you’d actually have a true black start?
thanks for the info.
jay
> On Sep 30, 2024, at 5:51 PM, Wayne Irwin via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> Hurricane Helene has taught us the hard way that Enphase batteries with anything other than IQ8's won't restart.
> The issue is that when the batteries try to restart (at the non-programmable time of 9:AM) if there are any significant loads, the batteries will not stay on long enough (300+ seconds) for any non-IQ8 micros to energize. The battery will attempt multiple times, but if there is a load, (such as a well pump) the draw from the load will essentially prohibit the batteries from energizing the micros long enough to engage and produce. The only solution is to have a load controller or turn off all loads once the power goes out. Otherwise, during these "attempts to turn on" power in the house will momentarily turn on and back off and potentially drain the batteries down to lower than the point of which they can even attempt to restart. I spoke at length with Enphase upper engineering (not tech support) about this today. They now know that most of the tech support staff does not know this important information.
>
> Once the batteries are dead, they are very difficult if not impossible to jump start with a generator. At the recommendation of tech support we tried multiple times with the "approved" inverter generator which ultimatly just wasted our time. Even though the controller/switch will accept the gen power and pass the energy to the loads, it will not energize the combiner or batteries. If your goal is to have an autonomous system with Enphase, it's only going to happen with the IQ8's (at this point).
>
> This is a significant issue with retrofitting older systems.
>
> By the way:
> - We've received numerous desperate calls from (orphaned) Powerwall owners whose systems also won't turn back on.
> - ALL of our Outback systems were issue free.
>
> I hope this helps some of you. Good Luck out there!
>
> Wayne Irwin
> President
> License #CVC56695
> State Licensed Solar Contractor
> Pure Energy Solar International Inc.
> Wayne at PureEnergySolar.com <mailto:Wayne at PureEnergySolar.com>
> PureEnergySolar.com <http://pureenergysolar.com/>
> SolarChargingStation.com <http://solarchargingstation.com/>
> 352 377-6527 Office
> 352 336-3299 Fax
>
>
> The Sun Is Always Shining!
>
> The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your computer system. Thank you.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240930/0471b771/attachment.htm>
More information about the RE-Wrenches
mailing list