I'm gonna add that the ASCO is the way to go. They offer both normal ATS
and with a service entrance rated breaker. I have dozens out there on GTBB
systems. What I really like about them is you can adjust a pot so that
there is little to no time delay in which the home switches over to
battery. Unlike a generator where you need a bit of time before the
connection. Clients have called to inform me that sometimes the switch over
happens so quickly their electronic devices aren't even aware of a grid
outage let alone the client themselves. That's my 2 cents.

Have a great weekend,
Christopher

On Fri, Sep 20, 2024 at 2:12 PM Kevin Pegg via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> We used to work with / recommend ASCO, but no longer. We had a site with
> dual ASC8000’s 400A 3 phase units switching between Gen 1 and Gen 2.
> Control board sensor problems arose and it failed to auto transfer back
> from Gen 2-1 due to sensor issues. Had to get client to open cabinet and
> affect a manual transfer.
>
>
>
> Despite having the extended warranty, they didn’t provide us service when
> requested. They also refused to sell us the board to replace. They didn’t
> refuse outright, just kept making appointments, failing to show up, one
> excuse after the other. The site was a 15 minute boat ride on a commercial
> water taxi and that was their latest excuse. Extremely unprofessional. We
> lost this client partially due to this.
>
>
>
> Kevin
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jerry Shafer via RE-wrenches
> *Sent:* September-20-24 8:45 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jerry Shafer <jerrysgarage01 at gmail.com>
> *Subject:* Re: [RE-wrenches] ATS Brand Recommendations
>
>
>
> Wrenches,
>
> If you are looking for a very good ATS, you need to look at ASCO that's
> what they do, from small less than 100 amp to high voltage multi 1000 amp
> units, they are a simple 2 wire start, l also use the Kohler products with
> no issues, l have AC Coupled off grid, DC Coupled on grid
>
> Fun times
>
>
>
> On Fri, Sep 20, 2024, 8:36 AM August Goers via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Hi Sam -
>
>
>
> It's been probably 6 or 8 years since I've selected a 3rd party automatic
> transfer switch, but we used to use Briggs & Stratton products with good
> results:
>
>
>
>
> https://energy.briggsandstratton.com/na/en_us/homeowners/products/standby-generators/transfer-switches-and-accessories.html
>
>
>
> At least at the time, these had internal circuitry to do the transfer
> between grid and offgrid operation with a pre-programmed delay of about 10
> or 20 seconds. We paired these frequently with Sunny Islands.
>
>
>
> Now that the major ESS manufacturers have Microgrid Interconnect Devices
> (MIDs) for their systems, we don't have any reason to use these.
>
>
>
> Best,
>
>
>
> August
>
> Luminalt
>
>
>
>
>
> On Fri, Sep 20, 2024 at 7:35 AM Sam Haraldson via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Wrenches,
>
>
>
> We are primarily a grid-tied solar EPC but like many solar companies have
> a long history with small off-grid installations.  In the past few years we
> have been tackling a handful of large, complex, grid-tied battery-backup
> systems (sub 90 kwh) range with some working flawlessly and some plagued
> with weekly quirks.  A weak link we've found in two of these installations
> was our choice to use Generac Automatic Transfer Switches.  In order for
> this ATS to sense a grid outage and perform its transfer it relies on
> circuitry built into a Generac generator as well as a source of 12v power
> (typically the generator start battery).
>
>
>
> One of our sites doesn't have a generator at all and the other does, but
> the grid sensing circuitry in the ATS is bypassed as we want the Sol-Arks
> to be the first-line of power during an outage and not the generator.  In
> order to accomplish this our electrician designed custom circuitry for grid
> sensing which is powered by a separate 12v source, has a 10 second delay,
> and flips the transfer switch during an outage placing the loads under the
> control of the Sol-Arks.
>
>
>
> Our initial design for these systems did not take into consideration that
> a Generac ATS doesn't have its own "brains" to grid sense and since we are
> now relying on a small custom circuit and a small external 12v power supply
> to act as a key player in an otherwise powerful and robust backup system we
> are second guessing our equipment choice.  What ATS solutions are Wrenches
> employing that we should be considering?
>
>
>
> TL;DR - what are the simplest ATS solutions that sense the grid
> (frequency, voltage, et al) and self-switch between backup and grid power
> automatically?
>
>
>
> Sincerely,
>
> Sam
>
>
>
>
>
> [image: OnSite Energy]
> <https://www.google.com/url?q=https://onsiteenergyinc.com/&source=gmail-html&ust=1677085494759000&usg=AOvVaw2NN36GoM1sjnS4RdC8Svt->
>
> *SAM HARALDSON *
>
> Operations Specialist
>
> (406) 551-6135
>
> 1515 N. Rouse Ave Bozeman, MT 59715
> <https://www.google.com/maps/search/1515+N.+Rouse+Ave+Bozeman,+MT+59715?entry=gmail&source=g>
>
> Locally owned and operated since 2012
>
> [image: B Corporation] <https://onsiteenergyinc.com/bcorp>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel 585-229-2083 or Cell 585-748-1870 *
*5115 S Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240920/973767be/attachment.htm>


More information about the RE-Wrenches mailing list