[RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid
scot.arey at solarcentex.com
scot.arey at solarcentex.com
Fri Sep 13 15:25:20 EDT 2024
Feedback to the group: utility replaced neutral from transformer to meter and all is fine. Utility didn’t give feedback but the Sol-Ark 120-volt during “off-grid” moved up to normal grid voltage of 124v when reconnected and its staying steady on both legs. Thanks for feedback! Scot
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Jason Szumlanski via RE-wrenches
Sent: Friday, September 13, 2024 7:41 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Jason Szumlanski <jason at floridasolardesigngroup.com>
Subject: Re: [RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid
By the way, you can test this yourself and possibly track it down to whether it's the meter base or the transformer connection. Shut off all loads and plug in a hair dryer to a 120V circuit. Measure the voltage. If it sags on that line and rises on the other, you have a loose neutral, but you still don't know if it's on the customer side or the utility side. Find a friendly neighbor on the same transformer. Ask them if they are having issues and offer to test their voltages to protect their appliances. Do the same at their house. This is how we tracked down an issue in Cape Coral, FL for a client and proved to the utility (who initially said the voltage was fine) that there must be something wrong at the pole. Sure enough - they found a melted tap connector on the neutral.
We would have never known, except the customer's Enphase System Controller was going haywire because it detected a line-side voltage issue. We probably saved a bunch of appliances for multiple utility customers.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Fri, Sep 13, 2024 at 8:35 AM Jason Szumlanski <jason at floridasolardesigngroup.com <mailto:jason at floridasolardesigngroup.com> > wrote:
Yep, sounds like a loose neutral either at the utility pole or the meter socket.
Around here the utility companies have a meter that they plug in to the socket that has two "hair dryers" internal to the meter to test for a loose neutral. They shut off the main disconnect to the house, plug in the test rig, and test the heating element on each leg. If there is a voltage sag/rise, it's a loose neutral somewhere. The voltage drop on one leg will be proportional to the rise on the other leg.
Look up "Super Beast from HJ Arnett Industries."
We had tons of these problems after Hurricane Ian. The linesmen from out of state who were assisting the locals were doing whatever it took to restore residential services, including using insulation piercing taps at the transformer. These don't meet the local service standards that require crimped connections. We saw plenty of people with destroyed appliances.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Fri, Sep 13, 2024 at 7:34 AM Peter Giroux via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:
Scot
We had this exact same thing happen last year with a 15. Voltage swings got pretty wild. It was a bad neutral in the meter base. Older meter base that had leaked and the neutral was a bar that compressed against the back of the base. Corroded and gunked up from the years of that small leak, needed a new meter base.
Peter Giroux
American Solar
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org> > On Behalf Of Scot Arey via RE-wrenches
Sent: Thursday, September 12, 2024 8:37 PM
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> >
Cc: scot.arey at solarcentex.com <mailto:scot.arey at solarcentex.com>
Subject: [RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid
I have Sol-Ark 15KW with 31kwh battery has been installed for year+.
Customer has for two days been having grid voltage issue seen as dimming lights. No neighbors reporting issues. He called his electrician who noted one high conductor and the other low. Have seen this before unrelated to solar and it was a bad neutral. His electrician says ok.
Customer disconnects from the grid because the fluctuations so severe and when he does, voltage issues go away and Sol-Ark is rock steady at 120-volts per leg. I send my senior tech over to ensure we don’t have a loose neutral or any grid conductors to the grid input. Nothing found.
Picture attached of grid voltages from the Sol-Ark monitoring (very helpful, I might add.)
The electric cooperative is sending a tech out tomorrow. Any body have insight or history with this?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240913/c8dab0f9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 42 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240913/c8dab0f9/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 148793 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240913/c8dab0f9/attachment.png>
More information about the RE-Wrenches
mailing list