[RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid
drake.chamberlin at redwoodalliance.org
drake.chamberlin at redwoodalliance.org
Fri Sep 13 06:33:32 EDT 2024
Check for voltage fluctuation at the main lugs, right where the service
cable comes in from the meter.
---
_Drake Chamberlin_
_Athens Electric LLC_
_Ohio Electrical Contractor's License 44810_
_NABCEP Certified PV Installation Professional_
On 2024-09-12 21:54, Kirpal Khalsa via RE-wrenches wrote:
> Scot,
> We have had numerous SolArk 15k's with loose neutrals direct from the
> factory. Double check all the factory connections in the accessible
> wiring compartment. I brought it to their attention each time I found
> it. They said they would do better on quality control bit obviously
> never heard back after that.
> Keep us posted what you find.
> Thanks
>
> Kirpal Khalsa
> Oregon Solarworks
>
> On Thu, Sep 12, 2024, 6:41 PM Blake Gleason via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Definitely sounds like a loose neutral on the utility side (likely at
> the pole/tap).
>
> I suspect if you turn off and disconnect the Sol-Ark the light
> flickering, etc will continue (until the utility recrimps their
> neutral...)
>
> Blake
>
> On Thu, Sep 12, 2024 at 5:38 PM Scot Arey via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> I have Sol-Ark 15KW with 31kwh battery has been installed for year+.
>
> Customer has for two days been having grid voltage issue seen as
> dimming lights. No neighbors reporting issues. He called his
> electrician who noted one high conductor and the other low. Have seen
> this before unrelated to solar and it was a bad neutral. His
> electrician says ok.
>
> Customer disconnects from the grid because the fluctuations so severe
> and when he does, voltage issues go away and Sol-Ark is rock steady at
> 120-volts per leg. I send my senior tech over to ensure we don't have a
> loose neutral or any grid conductors to the grid input. Nothing found.
>
> Picture attached of grid voltages from the Sol-Ark monitoring (very
> helpful, I might add.)
>
> The electric cooperative is sending a tech out tomorrow. Any body have
> insight or history with this?
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
>
> Blake Gleason, PE | Employee Owner
> Director of Innovation and Technical Excellence
> O: 510-845-2997 x128
> C: 510-867-5878
>
> [1]
>
> [2]
>
> 1035 Folger Ave. [3]
> Berkeley, CA 94710 [3]
> www.sunlightandpower.com [1]
> License #326203
>
> [4] [5] [6] _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://www.sunlightandpower.com/
[2] https://linktr.ee/SLP_Socials
[3]
https://www.google.com/maps/search/1035+Folger+Ave.+Berkeley,+CA+94710?entry=gmail&source=g
[4] https://benefitcorporationsforgood.com/
[5] https://www.amicussolar.com/
[6] https://calssa.org/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240913/5cac1f0c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240913/5cac1f0c/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240913/5cac1f0c/attachment.gif>
More information about the RE-Wrenches
mailing list