[RE-wrenches] Fm100’s stuck at full charge

Chris Sparadeo sparadeo.chris at gmail.com
Sat Sep 7 21:06:31 EDT 2024


Which Mate are you using? I know the FM100 is only compatible with the Mate
3s. If you are using a Mate 3, this mismatch could possibly be the cause of
these issues.

On Sat, Sep 7, 2024 at 7:25 PM Maverick Brown via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Dana
>
> I have always wired the PV negative all the way to the charge controller.
> That way, the battery negative of the charge controller that happens to go
> to a shunt has a proper representation of the current flow.  I guess you
> could put that PV negative at the same side of the shunt as the battery
> negative since internally the negatives are tied together on the charge
> controller.
>
> Did the charge controller come
> AFCI? If so, you likely have to bring both PV cables through the current
> sense of the AFCI.
>
> Also check to see if you have global charge control coordination turned
> on, if so, turn it off  and also check restart mode to set to two which
> means restart after 90 minutes no matter what.
>
>
> Thank you,
>
> Maverick
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
>  • Solar Commander Remote Power
>  • SunFlow Systems Cathodic Protection
> maverick at mavericksolar.com
> 512-460-9825
>
>
>
> On Sep 7, 2024, at 5:50 PM, Dana Orzel via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> OK, you wise guys.
>
>
> I am upgrading my home off grid system from two FM 80s to two FM 100s.
> The FM 80s were able to share the negative wire so you didn’t have to pull
> a second negative wire.
> I wired the FM 100 typical of how my FM 80s were wired with a number four
> battery negative assuming and yes, I know what happens when I assume, that
> the PV negative on the battery negative are common and I could just pull
> one number four since going through those double 1” - 90° is a bitch.
> Currently I have two # fours for output to battery, the number eight ground
> and 1 # six PV input.
> I got this all together and it’s charging just fine but once the battery
> got full charge controllers continued to produce full output. The battery
> dropped to a float and I had 2800W on each charge controller continuing to
> be produced at which was turning into heat so the FM 100s were getting very
> warm. The fans had not turned on, but the heat sinks were definitely very
> very warm to the touch. The battery voltage is fine.
> I Read the manual it doesn’t talk about being able to use one negative so
> I am assuming that my problem is that the PV needs a negative and they do
> not share the negative.
> Has anybody else seen this or done the same wiring maneuver.
> thanks in advance
>
> Dana Orzel - dana at solarwork.com - 208.721.7003
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240907/9b9a38c3/attachment.htm>


More information about the RE-Wrenches mailing list