[RE-wrenches] Sol-Ark 15K AC Coupling

pgiroux at mindspring.com pgiroux at mindspring.com
Sat Aug 24 17:43:30 EDT 2024


Jason

 

  Have recently had some similar issues. Ac coupling for the Sol-Ark really need to be on the gen inputs and I am told that Sol-Ark does do frequency shift on the gen inputs if needed. There is a programing button to turn it on, on one of the screens

 

  Please check to make sure all of your Sol-Arks have the same software / firmware . If they are not the same units will shut off. Had a situation that took multiple visits and multiple techs that turned out to be this. 

 

  Good luck with it, should work fine one you move the outputs of your solar to the gen inputs.

 

Peter Giroux

American Solar

 

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Jason Szumlanski via RE-wrenches
Sent: Saturday, August 24, 2024 5:07 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Jason Szumlanski <jason at floridasolardesigngroup.com>
Subject: Re: [RE-wrenches] Sol-Ark 15K AC Coupling

 

Good information. Thank you. 

 

I don't believe the Sol-Ark is capable of tapering AC coupled sources. It is either on or off. I know if you connect an AC coupled source to the GEN input(s) you can change the set points for when AC coupling starts and stops based on battery voltage or state of charge. However, it is unclear how these inverters manage AC coupled sources when connected on the load side. It does not appear to be documented when the inverter will shift the frequency to turn off the AC coupled source when it is connected on the load side. 

 

Anyway, I think I'm going to go ahead and move the AC coupled source to the GEN terminals. This will provide more positive control hopefully where I can shut down the AC coupled source when the battery reaches 90% state of charge and turns back on when it dips below 70% or 80%. 

 

If I need to put a smart load panel in, I can rig up a custom solution with a voltage sensitive relay and contactor feeding a subpanel. The only smart load capability I am looking for is to limit golf cart charging and operation of a specific air conditioning unit when battery capacity is low. It should be pretty easy to put something together to drop those loads when necessary. It would be great if these inverters had low voltage auxiliary relays to handle this logic. 

 

Jason 

 

 

 

 

 

On Sat, Aug 24, 2024, 3:32 PM pieter offgridenterprises.org <http://offgridenterprises.org>  via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:

Jason, You might need some more sophisticated equipment to diagnose the problem. It is possible that the Enphase system is not responding correctly to the Solark frequency adjustments as the battery gets full. We use our power analyzer to diagnose these sorts of issues, The power analyzer is an expensive piece of equipment so not many installers use them. Depending on the ”grid tied inverter” brand and the loads being operated at the site all sorts of site-specific anomalies can occur. With Solark specifically sometimes enabling things like active power factor correction can help. I realize that at times AC coupling is the most viable solution but generally speaking we avoid it wherever possible. I have never witnessed AC coupled systems control the grid tied inverters in a proportional way, the systems I have witnessed operate in a stepped manner. If the site loads are less than the Enphase output capacity, and the batteries are at a high state of charge you can potentially have power factor issues and see the Enphase system output power swing up and down. 

               If you monitor the system, it is possible that the Solark inverters are commanding the IQ8A inverters to reduce power and eventually shut down, but the Enphase system is not responding correctly. Have you looked to see if the Solark system is adjusting? If so, have you verified the Enphase system is responding ? If the battery voltage is staying within the limits, you set it is possible that the Enphase system is not responding, and the Inverter is shutting down to protect the batteries.

Pieter Huebner

Project Manager

Off grid Enterprises

 

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org> > On Behalf Of Jason Szumlanski via RE-wrenches
Sent: Saturday, August 24, 2024 1:32 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> >
Cc: Jason Szumlanski <jason at floridasolardesigngroup.com <mailto:jason at floridasolardesigngroup.com> >
Subject: [RE-wrenches] Sol-Ark 15K AC Coupling

 

Hi all,

 

Over the last three days I have had one of this infuriating and frustrating experiences with Sol-Ark where you talk to 3 people and get 10 different answers. At least I think I finally got the right one today. Here is the scenario and problem I was experiencing:

 

At a (very) remote location that is a boat ride away, I have three 15K inverters paralleled in a 120/240V system, off-grid, generator connected to the grid input (but not being used). The PV array connected to the DC inputs totals 40kW split across the three inverters. There is a 9.7kW Enphase system (8.4kW AC inverter rating) connected on the load side of the inverter outputs. Massive battery - 110kWh. Everything has been working well for a couple of weeks since we got it set up.

 

Then, over the last three days, we began experiencing unexpected shutdowns where the inverter would repeatedly stop inverting and PV would stop charging. There was usually no indication of errors on the screen. Everything was just stopped, but the inverters remained on. Sometimes they would restart once, only to shut down again relatively quickly. We had to manually restart the inverters with the ON/OFF buttons. Then we started getting various errors, with F50 being the strange one that is not documented. I reached Sol-Ark, and they said the F50 points to an AC input issue, but the generator was not on, so that didn't make sense. I was on my own to double-check all of the wiring.

 

But there was also an F41 Parallel System Stop error, which pointed me to that suggested cause. I realized that one of the inverters had a -1725 COMM firmware, whereas the others had -1726. I don't know how that happened because I'm certain that I had them all on the same firmware at one time. Anyway, I spent all day yesterday trying to reach Sol-Ark and getting the firmware to match. I thought we had the issue resolved by the time I left, as I was able to run the system for an hour without a shutdown.

 

Then I got a call at noon today from the owner. Same problem. System shut down.

 

I was able to reach Sol-Ark immediately this time and the agent gave me a more plausible answer. He said the F50 error points to something wrong with the AC coupling. We started to put our heads together and I realized that this issue first popped up around mid-day on Thursday, and then repeated itself mid-day on Friday. Here we are again today, and I get the call at noon. It seems like the issue happens as soon as the batteries reach 100% capacity. It's like the Sol-Ark is not commanding the IQ8A microinverters to shut down. I had the owner shut off the AC coupling input breaker and I remotely unchecked the box for AC coupling on the load side. That seems to have resolved the issue.

 

Ok, fine, but how do we resolve this (I asked Sol-Ark)? The "solution" I was offered is to move the AC coupled input to the GEN terminals. The problem is that I need to reserve the GEN terminals for an upcoming Smart Load subpanel. That's why I installed the AC coupling on the load side, which is a documented and accepted practice.

 

I do have AC coupling working without issue on a grid-tied system at another location with dual Sol-Arks, but that is connected to the GEN terminals. This is the first time I have AC coupled on the load side. Has anyone successfully AC coupled on the load side, particularly with microinverters? 

 

I'm probably going to have to climb the customer service ladder at Sol-Ark to get a resolution for this, but I wanted to get some feedback in case someone has already been down this road.

 

Thanks in advance,

 

Jason Szumlanski

Florida Solar Design Group

 

 

 

 

 

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240824/46c229f6/attachment.htm>


More information about the RE-Wrenches mailing list