[RE-wrenches] OB Radian / FM60 grid tie mystery

Dave Angelini Offgrid Solar offgridsolar at sti.net
Sun Aug 18 19:51:15 EDT 2024


You are all the Outaback wrenches but with Schneider before you reset 
the defaults, you should just do a complete DC power down.  Just in case 
it is a stuck bit in config.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
    [2]https://offgridsolar1.com/ [3]  [2]
e-mail  offgridsolar at sti.net
text 209 813 0060

On 2024-08-18 4:20 pm, Jay via RE-wrenches wrote:

> One other thing that has worked for weird issues is a full factory 
> reset of everything.
> 
> Jay
> 
>> On Aug 18, 2024, at 4:18 PM, Maverick Brown 
>> <maverick at mavericksolar.com> wrote:
> 
> On OpticsRE go to devices, Mate3S, Global Charge. Disable everything 
> there and for good measure also set the Maximum Battery Charge to 
> generously large number.
> 
> Also, if you recently upgraded to Inverter software 1.6.63 or later, 
> you have to do some procedure to edit the maximum sell current
> 
> <preview.png>
> 
> upgrading_1_6_63_app_note [1]
> PDF Document · 200 KB [1]
> 
> Thank you,
> 
> Maverick
> 
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
> * Solar Commander Remote Power
> * SunFlow Systems Cathodic Protection
> maverick at mavericksolar.com
> 512-460-9825
> 
> On Aug 18, 2024, at 3:59 PM, Kirk Herander via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Looks like its only programmable directly on the Mate3s, not in optics 
> RE. Or maybe I haven;t found it yet.
> 
> On Sun, Aug 18, 2024 at 3:22 PM Jay <jay.peltz at gmail.com> wrote:
> 
> There is a setting called
> 
> FLEXnet dc advanced control.
> 
> Default is Y
> 
> I always set it to N
> 
> Pg 128 in my manual.
> 
> Jay
> 
> On Aug 18, 2024, at 11:11 AM, Kirk Herander via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Hello All,
> .
> I have a Radian 8048 system in service for over 10 years now. It sold 
> back quite normally until the last several months -3.- FM60 CC's are 
> set to grid tie mode and  viewable and programmed from the Mate3s / 
> OpticsRE. This issue loosely correlates to replacing one of the CCs 
> several months ago.
> 
> Trouble is all -3- charge controllers are almost always in a float 
> mode. The radian does sell, but at a small KW compared to what it used 
> to before the frequent float mode started popping up. If I remember 
> correctly, ideally the CCs should always be in bulk charge when 
> sellback occurs.
> 
> I have the CC and inverter charger float set to about 1 vdc higher then 
> the inverter's sell volts, as I believe was recommended way back when. 
> Hard to understand what changed, but something did. I've checked the 
> relevant setpoints many times and can't find anything obviously amiss.
> 
> Does a sell mode tech note paper exist still for the Radian system? Did 
> it ever? Any ideas would be greatly appreciated.
> 
> --
> 
> Kirk Herander / kirkh at vermont.solar
> 
> Owner|Principal, VT Solar, LLC
> 
> _Celebrating our 33st Anniversary 1991-2024!!_
> 
> dba Vermont Solar Engineering
> 
> 802.559.1225 _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

   --

Kirk Herander / kirkh at vermont.solar

Owner|Principal, VT Solar, LLC

_Celebrating our 33st Anniversary 1991-2024!!_

dba Vermont Solar Engineering

802.559.1225 _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] 
https://www.outbackpower.com/downloads/documents/appnotes/upgrading_1_6_63_app_note.pdf
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240818/b0f2c1ab/attachment.htm>


More information about the RE-Wrenches mailing list