[RE-wrenches] KiloVault Issues

Jay jay.peltz at gmail.com
Tue Jul 30 14:55:22 EDT 2024


I’m wondering if the batteries are out of balance. You might need to charge 1 set alone or even individually to get them full and calibrated. 

I had someone with a different kilovault have similar issues which when we charged them individually took care of the problem. And guessing it will come back at some point. 

The other thing I just remembered is that there are balancers from a few companies that I’d recommend ( so does kilovault). 

Kilovault and victron are the two that come to mind but are probably others. 

Jay

> On Jul 30, 2024, at 12:36 PM, Maverick Brown via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Chris
> 
> Lots of variables here. 
> Is this system on grid or off grid?
> 
> 8 of those batteries wired in series / parallel would be about 30kWh gross capacity. 4 x 12Vnom x 300Ah x 2 sets. About 51.2 x 300 x 2 x 80% = 24.6kWh usable. 
> 
> What are the charge settings? Load profiles? Etc. 
> 
> Do you have access to MySolArk.com for that customer to see how things are going? Do the batteries get charged (about 3.45V per cell each day or six)? How low do they get each day? Does the generator auto start on time? 
> 
> 
> Thank you,
> 
> Maverick
> 
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
>  • Solar Commander Remote Power
>  • SunFlow Systems Cathodic Protection 
> maverick at mavericksolar.com
> 512-460-9825
> 
> 
> 
>>> On Jul 30, 2024, at 12:57 PM, Chris Daum via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>> 
>> Any ideas on what might be ailing our KiloVault LiFePo4 3600HLX+ batteries?
>> Customer has 8 of the 3600HLX+ (300ah).  New outta the box and they aren't
>> holding charge. We hear that KiloVault is out of business?  Inverter is the
>> Sol-Ark 15K.  Insights on what we can do and other ideas that can provide a
>> direction will be appreciated.  Generator is 20KW Generwreck...er...Generac.
>> The installer is the customer's electrician.  Thanks so much!
>> 
>> Best,
>> 
>> Chris Daum
>> Oasis Montana Inc.
>> 406-777- 4321
>> 406-777-4309 fax
>> www.oasismontana.com
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240730/f8c9429f/attachment.htm>


More information about the RE-Wrenches mailing list