FYI Sol Ark sales engineer has suggested the following:
“For the 15K, we've recommended AcuCT R Series - AcuCT-4161R-800:100mA |
Accuenergy <https://shop.accuenergy.com/product/acuct-4146r-800a-100ma/> with
100mA output.
On the inverter, you will need to adjust the CT ratio to 8000:1. Also note
that this will have to be confirmed with Tech Support upon
installation/commissioning, to prevent void of warranty.”
The CT has an ID of 4” so all parallel conductors should pass through just
fine.
The 30 and 60K units use a similar Accuenergy CT but higher amp draw that
are not compatible with residential units.
On Thu, Jul 18, 2024 at 11:51 AM Dan Lepinski, P.E. <Dan at ntree.org> wrote:
> Chris,
>
> If the only goal is to avoid backfeeding the grid, in the configuration
> as described, the inverter will sense any outbound current and reduce its
> output accordingly.
>
> Should you desire to monitor incoming power and energy, all readings will
> need to be multiplied by three .. which unless there's a specific setting
> in the inverter to automatically allow this scaling (unlikely, and requires
> Sol-Ark verification), such multiplications will need to be consciously
> performed when looking at the data.
>
> Not ideal from a data tracking perspective, but it will at least meet the
> zero-backfeed stipulation. (You may want to discuss adding bi-directional
> CT "current scaling" capability with Sol-Ark if it doesn't already exist in
> their firmware.)
>
>
> Dan
>
>
>
> On 7/18/24 10:24, Chris Sparadeo wrote:
> > Hi Dan,
> >
> > Thanks for your thoughts. The idea of 1/3 CT crossed my mind as well.
> The question is how to set up the inverter with a 3x multiplier on those
> two CTs to get a full 800A reading. I assume that would be something a Sol
> Ark engineer would have to program remotely?
> >
> > Thanks again,
> >
> > -Chris
> >
> > On Thu, Jul 18, 2024 at 8:42 AM Dan Lepinski, P.E. <Dan at ntree.org
> <mailto:Dan at ntree.org>> wrote:
> >
> > Gentlemen,
> >
> > A possible solution is to utilize one CT around one each of the
> three paralleled 400 MCM. One CT around one of the three L1 conductors,
> and the other CT around one of the three L2 conductors. Ensure correct
> direction for current flow when you install them. (Sol-Ark calls it
> "polarity".)
> >
> > With three 400 MCM in parallel, each conductor will carry nominally
> 1/3 of the total current, regardless of direction (in or out). Thus a CT
> around each of the three phase conductors will measure 1/3 of the total
> current.
> >
> > 800 Amps / 3 = 266.67 amps.
> >
> > As you probably know, there's a 200 amp CT and 600 amp CT on
> Sol-ark's website. https://shop.sol-ark.com/catalog/extra-large-cts/ <
> https://shop.sol-ark.com/catalog/extra-large-cts/>
> >
> > Obviously the 200 amp CT isn't suitable (267A > 200A), which leaves
> the 600 amp part.
> >
> > Program the inverter accordingly, with an understanding the 600 A CT
> will be reading 1/3 of the total current.
> >
> > You'll give up some resolution (267A/600A = 44.4% of the total
> full-scale current reading for a 600 amp CT), but with proper inverter
> setup, it will work for purposes of limiting export.
> >
> > That said .. each CT requires its own burden resistor, and the
> inverter isn't designed for three to be connected as you're discussing,
> whether series or parallel.
> >
> >
> > Hope this helps...
> >
> >
> > Dan
> >
> >
> > --
> > Dan Lepinski, P.E.
> > Professional Solar Consultant & Electrical Design Engineer
> > Serving the Solar Industry Since 1972
> > www.ntree.org <http://www.ntree.org>
> > 817.884.6081 (cell)
> > Texas License 123654
> > Texas Registered Firm F-17965
> >
> > * United States Department of Energy National Building Codes
> Assistance Project
> > (One of only two engineers selected nationwide for the program.)
> >
> > * Voting Member - UL 1741 / UL 62109 Standards Technical Panel
> >
> > * Voting Member - IEEE 1547 Standards Development Committee
> >
> > * Voting Member - North Central Texas Council of Governments
> Regional Codes Coordinating Committee
> >
> > * Voting Member - North Central Texas Council of Governments
> Electrical Code Advisory Board
> >
> > * State of Texas Energy Advisory Council Member
> >
> > * State of Texas Contracted Subject Matter Expert on Solar Energy
> >
> > * International Code Council Preferred Education Provider (#2882)
> >
> > Professional Profile:
> https://www.linkedin.com/in/dan-lepinski-p-e-5339bb22/ <
> https://www.linkedin.com/in/dan-lepinski-p-e-5339bb22/>
> >
> > "Scientists investigate that which already is; engineers create that
> which has never been."
> > ~ Albert Einstein
> >
> > Unless indicated otherwise, all information contained in this
> message is privileged and confidential. As such, it is intended only for
> use by the addressee(s) named above, and others who have been specifically
> authorized to receive it. Correspondence designated as privileged and
> confidential is subject to all terms and conditions of any Confidentiality
> Agreements and/or Non-Disclosure Agreements in effect between our
> respective parties.
> >
> >
> >
> >
> > >
> >
> > > On Thursday, July 18, 2024 at 07:04:47 AM CDT, Kirk Herander via
> RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:
> re-wrenches at lists.re-wrenches.org>> wrote:
> >
> > >
> >
> > >
> >
> > > As an aside, I ran into this with a Fortress True 12kw. (As of
> several months ago) They have not tested parallel CTs, nor have they tested
> single CTs in any service above 200A. They would not approve my plan to
> parallel CTs on a parallel conductor, 400A service.
> >
> > >
> >
> > > Fortress does have an input for a 3rd party meter, who knows if
> it's been developed, maybe Sol-Ark does too.
> >
> > >
> >
> > > Definitely run it past Sol-Ark first.
> >
> > >
> >
> > >
> >
> > >
> >
> > > On Thu, Jul 18, 2024 at 7:46 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org <mailto:
> re-wrenches at lists.re-wrenches.org>> wrote:
> >
> > > You should be able to parallel 6 CTs (3 per phase) as long as you
> get the phases and directions right. The question really comes down to
> whether the Sol-Ark can handle the current from 800A at the CT ratio (which
> I believe is 2000:1). For practical purposes, on an 800A service,
> particularly residential, you will probably never see more than 600A, so it
> would probably be fine.
> >
> > >
> >
> > > But I would like to know what Sol-Ark says about this. It does not
> appear to be documented. For the 30K and 60K they have recommended CTs for
> up to 1200A. I'm not sure if 600A measurement is a hard limit for the 15K
> considering that's the largest single CT they specify in their
> documentation.
> >
> > >
> >
> > > Jason
> >
> > >
> >
> > >
> >
> > >
> >
> > > On Thu, Jul 18, 2024, 7:23 AM Chris Sparadeo <
> sparadeo.chris at gmail.com <mailto:sparadeo.chris at gmail.com>> wrote:
> >
> > > Hi Jason,
> >
> > >
> >
> > > Sorry for not clarifying. This is a export limited scenario, so
> CTs would still be required.
> >
> > >
> >
> > >
> >
> > >
> >
> > >
> >
> > > On Thu, Jul 18, 2024 at 6:51 AM Jason Szumlanski <
> jason at floridasolardesigngroup.com <mailto:
> jason at floridasolardesigngroup.com>> wrote:
> >
> > > This may or may not be helpful, but are you sure you need the CTs?
> They are not always required. You would need them for power export limiting
> or grid peak shaving, but for straight grid-tied with or without battery
> backup, you don't need them.
> >
> > >
> >
> > > Jason Szumlanski
> >
> > > Florida Solar Design Group
> >
> > >
> >
> > >
> >
> > >
> >
> > > On Wed, Jul 17, 2024, 8:41 PM Chris Sparadeo via RE-wrenches <
> re-wrenches at lists.re-wrenches.org <mailto:
> re-wrenches at lists.re-wrenches.org>> wrote:
> >
> > > Hey there wrenchers,
> >
> > >
> >
> > > I am working on a larger project with 6 Sol-Ark 15K units and an
> 800A service. The main service conductors are 3 parallel runs of 400 kcmil.
> I am wondering how to CT these conductors from the master inverter. Sol Ark
> tech support has not been very helpful so far. I have the included 300A CTs
> ....and I do know that they make a 600A CT, but its physical size and
> rating aren't a good fit. Does anyone have experience with either a Sol Ark
> or third party CT that might fit this 800A configuration?
> >
> > >
> >
> > > Kindly,
> >
> > >
> >
> > > Chris Sparadeo
> >
>