[RE-wrenches] Sol-Ark with 800A Service
Chris Sparadeo
sparadeo.chris at gmail.com
Thu Jul 18 07:23:32 EDT 2024
Hi Jason,
Sorry for not clarifying. This is a export limited scenario, so CTs would
still be required.
On Thu, Jul 18, 2024 at 6:51 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> This may or may not be helpful, but are you sure you need the CTs? They
> are not always required. You would need them for power export limiting or
> grid peak shaving, but for straight grid-tied with or without battery
> backup, you don't need them.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
>
> On Wed, Jul 17, 2024, 8:41 PM Chris Sparadeo via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hey there wrenchers,
>>
>> I am working on a larger project with 6 Sol-Ark 15K units and an 800A
>> service. The main service conductors are 3 parallel runs of 400 kcmil. I am
>> wondering how to CT these conductors from the master inverter. Sol Ark tech
>> support has not been very helpful so far. I have the included 300A CTs
>> ....and I do know that they make a 600A CT, but its physical size and
>> rating aren't a good fit. Does anyone have experience with either a Sol Ark
>> or third party CT that might fit this 800A configuration?
>>
>> Kindly,
>>
>> Chris Sparadeo
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240718/8586618f/attachment.htm>
More information about the RE-Wrenches
mailing list