[RE-wrenches] VFD drives

Michael Morningstar mjmorningstar at gmail.com
Thu Jul 11 13:11:49 EDT 2024


I’ve years of experience running vfds on generator power. No issues.
Personally, I run numerous old cast iron woodworking machines that all have
5 and 10hp 3p motors with VFDs from a 15kw Kubota open frame generator. 15
second ramp up time. And my generator is single phase.

On Thu, Jul 11, 2024 at 10:06 AM jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> HI All,
>
> I’m being asked to comment about running a 10hp 3 phase well centrifugal
> pump off of a 30kw single phase generator with a VFD drive.
> This well pump is located in a tank for fire fighting applications, so its
> not down a deep well meaning almost no head pressure. And the start time
> can be quite slow as its not supplying a house/pressure tank.
>
>
> I”m not an expert on VFD drives, but I figure many of you are.
>
> My question, based on the question from the engineer is:
>
> 1. is there any issue with running a VFD off of a good quality 30kw brand
> new Kohler turbo propane generator?
> The engineer seems to think there is but he won’t say why.
>
> i can’t think of any reason at all?
>
> This generator is only running this one load, the well pump.
>
> jay
>
>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

Michael Morningstar


Morningstar Electric Inc

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

CSLB 1116835

mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240711/3d613103/attachment.htm>


More information about the RE-Wrenches mailing list