Hi,
There are several different ways to accomplish this via RF signalling.
One discussed before here is to use the IO-WRP kit from supplyhouse.com. I
did exactly what you want (disconnecting an inverter feed remotely when the
generator started) using this kit and relay / contactor.
And check out offerings at https://www.rfsolutions.co.uk/. I just set up a
wireless genny start / stop from the dry contact of a Fortress Envy, with
one of their xmitter (Bogeyboard) and receiver (Quanta) pairs. @ about 1/2
the price of the IO-WRP setup.
The Rfsolutions stuff is quite versatile, just about anything can be told
to turn on or off, based on one or more 0v inputs. A wide variety of
function inventory to choose from.
A found the products I needed in stock at Digikey and Mouser, respectively.
On Thu, Jun 20, 2024 at 2:35 AM William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Friends:
>
>
>
> I have an installation of 12 Enphase IQ inverters that is downstream from
> a generator transfer switch. During power outages the generator will run
> poorly when the Enphase is on and the sun is shining. The problems go away
> when the Enphase is shut off. No surprises about this.
>
>
>
> The Enphase is installed on a barn about 150 conduit feet from the
> generator transfer switch. My plan is to create a low voltage signal when
> the generator is running and send it to a coil on a contactor in the barn.
> Said contactor will disconnect the 12 micro-inverters.
>
>
>
> There is existing one 26 AWG pairs of a Cat 6 cable running between the
> buildings. I have found a two pole, 30A contactor that draws 7 watts on
> the coil. The voltage drop calcs on 150 feet of 26 AWG wire shows a 24
> volt signal will not cause excessive voltage drop (~4%).
>
>
>
> Here is where I am uncertain: Should I run 24 volts AC or DC? My concern
> about DC is if there are any damp connections, electrolysis will occur that
> might erode the 26 AWG conductors. We’ve all seen powder where copper used
> to be. Is AC less susceptible to electrolysis? My research has turned up
> no pertinent conclusions.
>
>
>
> Thanks in advance.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
*Owner|Principal, VT Solar, LLC*
*Celebrating our 33st Anniversary 1991-2024!!*
dba Vermont Solar Engineering
802.559.1225
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240620/6bce5585/attachment.htm>
More information about the RE-Wrenches
mailing list