Let me say I think the idea is generally bad.  Your client would need to be
actively involved managing this system on an hour by hour basis or both
battery banks are likely to be ruined.  If you want to switch between
batteries, unless both battery arrays are at a very similar voltage (+/- 0.5
volts) you should not parallel them.  In that scenario you would need to
shut down the inverter(s), switch battery banks, then restart the inverter.
A breaker interlock may be in order to prevent bad things from happening.
Like I said, a bad idea.  If you have too much battery to match the PV
capabilities you need to reduce the battery bank capacity.

If this system includes valid BOS components, and you still want to
experiment, integrate within that system by adding a battery breaker.  If it
does not have a decent BOS (Outback Flexware, Midnite DC breaker panel, for
example) that is a problem in itself.  Add the BOS.  The PV charge needs to
have either two battery breakers or be wired on the inverter side of the
battery breaker, an arrangement that I do not recommend.

Did I mention I think this is a bad idea?

William Miller

Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985



-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of greg egan via RE-wrenches
Sent: Saturday, June 15, 2024 10:18 AM
To: re-wrenches at lists.re-wrenches.org
Cc: greg egan
Subject: [RE-wrenches] Dual battery bank switch for 48 VDC system

Wrenches,  I have a customer who has a 2 strings of AGM's @ 48 VDC that
we want to split so we can charge them at decent charge rate. Adding
more PV and/or larger generator and inverter is cost prohibitive.  I've
seen Blue Seas (#3002) 4 position 500 amp switches that are rated for
32VDC.  Max he could possibly pull at once with his system is less than
100 amps.

I would assume the Blue Seas 3002 would work and I'd probably use it in
my garage, but I'm not comfortable recommending it to a customer.  Any
suggestions on a 60 VDC rated unit that could handle say 150 amps and
4/0 cables?

Maybe I'm being too cautious since the max load would be < 6KW and the
3002 is rated for 16kW load (32 VDC /500A)?   Thoughts?

Thank you,

Greg Egan
Remote Power Inc.
Fairbanks, AK
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


More information about the RE-Wrenches mailing list