[RE-wrenches] Two Outback Radian 8048 fails in same week..what is likely wrong in 7+ year inverters?
Jerry Shafer
jerrysgarage01 at gmail.com
Mon Jun 10 01:15:02 EDT 2024
I have seen more power supply board stacks fail than inverters and of the
power supply stack it has been the top board more than others.
Funtimes
On Sun, Jun 9, 2024, 3:50 PM Scot Arey via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Longtime Outback user but since the experience of this group is so varied,
> I’ll say 8-years (so you real old-timers don’t laugh!).
>
>
>
> Here is the scenario of two systems:
>
>
>
> First is a full off-grid customer and we have two stacked 8048s, with four
> FM80s and a 14kw array that charges a RE2200. After a home fire (not
> related to the solar!) we got the system back on and it required heavy dual
> inverter operations to get the home going after a four-month hiatus. Looks
> like that slave inverter stopped working at end of the day after we
> re-powered and departed. He can operate with the single 8048.
>
> The second situation is a used 8048 I have at the Texas coast that powers
> a small duck/hunt bunkhouse. It was used system (and I’m a benefitting
> member) but worked just fine when I put in. Went down to check the
> batteries (FLA, as AGM nor lithium was in budget) and there was not
> inverter output and no indication on the MATE like an error code.
>
> S*o my question is – what typically fails in a 8048 from old age or heat
> stress?* Wanted to ask here since so many issues with Outback tech spt
> during its transition. Neither inverter is in warranty, but trying to field
> repair anything I might be able to.
>
> I do have battery voltage past the two 175A disconnects in the GSLC. No
> “thump” I typically get when the inverter first gets battery power and no
> lights.
>
> Any troubleshooting tips to identify the culprit part?
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240609/66939a38/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240609/66939a38/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240609/66939a38/attachment-0001.png>
More information about the RE-Wrenches
mailing list