[RE-wrenches] Sol-Ark 15k solar panel frame grounding
Mac Lewis
maclewis1 at gmail.com
Wed Jun 5 09:53:05 EDT 2024
Hi Jason,
You should be able to land your PV EGC in the inverter ground bar. You
could do a quick resistance check to verify the +, - PV
Is there a bond somewhere (upstream service panel or in the Sol-Ark itself)
between ground and neutral? If not, this can cause this fault.
On Wed, Jun 5, 2024 at 7:03 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Can anybody clarify the following instruction from the manual?
>
> "GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire"
>
> Does this mean do not connect the array equipment grounding conductor to
> the grounding terminal in the inverter? Where would be the suggested place
> to connect the equipment grounding conductor, and why does it make a
> difference? It would still be electrically bonded to the grounding terminal
> in the inverter.
>
> I'm asking because I do, in fact, have an equipment grounding conductor
> from the array connected to the ground terminal in the inverter at a home.
> I am getting an F08 GFDI fault. The manual doesn't say anything about the
> DC side with respect to this error. It suggests it is an AC current leakage
> to ground. But Sol-Ark tech support suggested that I disconnect the PV to
> rule it out as a source of the fault.
>
>
>
> Jason Szumlanski
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240605/49d05bd6/attachment.htm>
More information about the RE-Wrenches
mailing list