What specific UL listing(s) are they requiring? Around these parts it's
been UL 9540 for all AHJs, and some requiring that even for lead-acid,
despite the IFC exceptions and so few listed products (the IRC now seems to
require UL 9540 even if the system is not grid-interconnected). UL 9540A is
not an actual listing but an active fire test, results of which can be used
to gain their UL 9540 and/or allow smaller offsets between each ESS unit
and from windows, doors etc if their individual UL 9540A testing results
allow that.

Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
d <dan.fink at greendustrialtraining.com>anbob88 at gmail.com
970-672-4342




On Mon, May 20, 2024 at 5:22 PM jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> HI All
>
> I got a call from a fellow installer who needs a UL listed lithium
> battery.
> Say 30-50 kwh.  open loop as its working with existing OB radians.
> Could be outside or inside
>
> It so confusing to find the right battery I’d thought I would ask what
> folks are using/recommending.
>
> thanks
>
> jay
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240520/60937496/attachment.htm>


More information about the RE-Wrenches mailing list