[RE-wrenches] PWM Controllers in parallel

Andrew Perkins andrew at greenwired.com
Tue May 7 15:09:49 EDT 2024


Sorry yes for clarification that he wants to parallel the INPUTS I am aware of paralleling the outputs we do that all the time. Sorry for the confusion but seems like the census now says NO on paralleling the 2 inputs from one array. 


Andrew Perkins

Greenwired 

P: 707-923-2001 ext. 100

1150 #1 Evergreen Rd

Redway, CA 95560

http://www.greenwired.com














---- On Tue, 07 May 2024 11:58:37 -0700 Howie Michaelson via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote ---



Yes, output not input. Thanks for clarifying that William...

Howie


Sun Catcher

Solar Electric Systems Sales & Service
802-272-0004







On Tue, May 7, 2024 at 2:55 PM William Miller via RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org> wrote:

Andrew:

 

I see no problem paralleling the Charge Controller outputs but I would not parallel the inputs.  With parallel inputs, unless there is protection to prevent excessive current, there is a risk that one CC will take over and try to regulate the entire array.

 

I suggest you divide up the panels to create one appropriately sized discrete array into each CC.  You can parallel two strings of panels without OCPD.

 

William

 

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

http://www.millersolar.com/

CA Lic. 773985

 


 

From: RE-wrenches [mailto:mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Andrew Perkins via RE-wrenches
Sent: Tuesday, May 7, 2024 9:24 AM
To: Re Wrenches
Cc: Andrew Perkins
Subject: [RE-wrenches] PWM Controllers in parallel


 

Hello Wrenches,


                    I have a client who has a large 2000 watt 12v array that he said used to be hooked into an internal solar charger on his old trace. Never seen a trace with one of those in it but he claims it could do 200a. This internal charger has now died and needs a replacement. He is refusing to rewire his panels into a new configuration and their aren't many options for him out there. I did get him a Coleman Aire 400a Charge controller but it is more of a load controller and wants to be able to properly absorb is batteries off the sun. He currently has a c60 running only part of the array and now he is asking about running another c60 in parallel. Not quite sure if this would work or not but my gut feeling says no and there will be problems. 


 


If anyone knows of any controllers that would fit that or if running those in parallel works your advice would be greatly appreciated.  


 


Andrew Perkins

Greenwired

P: 707-923-2001 ext. 100

1150 #1 Evergreen Rd

Redway, CA 95560

http://www.greenwired.com











 




 



 



_______________________________________________
 List sponsored by Redwood Alliance
 
 Pay optional member dues here: http://re-wrenches.org
 
 List Address: mailto:RE-wrenches at lists.re-wrenches.org
 
 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 There are two list archives for searching. When one doesn't work, try the other:
 https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules & etiquette:
 http://www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 http://www.members.re-wrenches.org
 



_______________________________________________
List sponsored by Redwood Alliance 
 
Pay optional member dues here: http://re-wrenches.org 
 
List Address: mailto:RE-wrenches at lists.re-wrenches.org 
 
Change listserver email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 
There are two list archives for searching. When one doesn't work, try the other: 
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
 
List rules & etiquette: 
http://www.re-wrenches.org/etiquette.htm 
 
Check out or update participant bios: 
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240507/4e49bde6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 1596050015677007_1701277005.png
Type: image/png
Size: 16298 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240507/4e49bde6/attachment.png>


More information about the RE-Wrenches mailing list