[RE-wrenches] 120 Vac and 12Vdc mixed distribution system

John Blittersdorf john.blittersdorf at gmail.com
Wed Apr 24 13:51:59 EDT 2024


Jason,
  Just using the converter works fine. They are considered a battery
charger or a regulated power supply. I am currently running that way now
with the battery cables going nowhere.  I was thinking of putting the
battery back in the system just for triple redundancy when my inverter hits
low battery cutoff voltage on a cold winter night and no fuel for the
generator (or it won't start).
My Iota DLS puts out a regulated 13.4 volts up to 30 amps.

John

On Wed, Apr 24, 2024 at 8:25 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Ah ha! I didn't consider using a small 12V battery with a charger. I was
> thinking of just using a 120V -> 12V converter to handle the DC loads. Is
> the 12V battery really necessary, or can I just power the DC loads directly
> with a converter? If I just have lights and fans on the DC system, the load
> should be pretty minimal.
>
> I could use a separate 12V battery, but I would like to eliminate that
> cost and complexity if possible.
>
>
> And yeah, I am not considering this a money making opportunity. It's
> really just a challenge to ward off boredom from the daily grind.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Wed, Apr 24, 2024 at 8:01 AM John Blittersdorf via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Jason,
>>   I have a customer with the same situation except he already has a 12 V
>> VFX inverter,  He has a sunfrost fridge and other small loads with a very
>> fancy custom control board
>> originally set up to handle AC and DC systems.  We are adding a lot more
>> solar and I was considering a dual battery system but the owner didn't like
>> that idea.  We are going with and Iota 12v power supply (i use one at my
>> house for my sunfrost) to power up all his DC loads and will be adding a
>> large 48 V battery bank and over 4Kw of solar using a VFXR3648 directly in
>> place of the 12V inverter.  He complained that the existing inverter would
>> not handle all his current AC loads very well.  My own house is fully wired
>> for 12VDC as well as AC (lots of #10 copper not being used) and I have been
>> considering getting a small LFP 12V battery to put back on by DC System.
>> Then use the Iota as a secondary charging method with some of my large
>> stash of older modules hooked up for 12V direct with C40 charge controller
>> to recreate my original system just for kicks. I'm only using DC for my
>> Sunfrost and one "emergency light" in the livingroom right now.  For your
>> customer, a small LFP 12v battery (approximately $500 or less) to replace
>> his old battery bankm and more larger ones for the new AC side with 48V
>> inverter fed by his generator or through an Iota 48 V charger ifusing a
>> smaller non charging inverter. Unlike Dave, I like these challenges. Maybe
>> thats why I never seem to make money.!!
>>
>> John Blittersdorf
>> offgridvermont.com
>>
>>
>> On Wed, Apr 24, 2024 at 7:22 AM Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Fortunately, the owner is pretty handy and is willing to live with any
>>> negative consequences. That said, I want to offer him something as simple
>>> and bulletproof as possible. I am walking into this with eyes wide open,
>>> for sure.
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>> On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via
>>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> Not being helpful but I  walk away from these.  It will come back to you.
>>>>
>>>> *Dave Angelini Offgrid Solar
>>>> "we go where powerlines don't"
>>>>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/>  <http://members.sti.net/offgridsolar/>
>>>> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
>>>> text 209 813 0060*
>>>>
>>>>
>>>> On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:
>>>>
>>>> I have an off-grid client who is working on replacing old equipment at
>>>> a cabin. He has a lot of 12 volt distribution in the house for lighting,
>>>> fans, and a 12 volt refrigerator. He also has 120 volt AC loads that run
>>>> through a separate distribution panel where the only source is a 2000 Watt
>>>> Honda generator. There is no inverter present. The batteries are charged
>>>> through a Trace C40.
>>>>
>>>> He currently has a few ancient solar panels and a struggling Bank of
>>>> AGM batteries. It's time for an upgrade. I can easily supply enough PV
>>>> power for what he needs. He currently has a 9 kilowatt hour battery
>>>> capacity that he was happy with when the batteries operated optimally.
>>>> Nonetheless, I would probably future-proof him with a 10 to 15 kilowatt
>>>> hour LiPo to double or triple his usable capacity.
>>>>
>>>> For convenience, obviously it would be nice to have an inverter to
>>>> eliminate or reduce the generator requirement. But he seems committed to
>>>> keeping his 12 volt distribution because it would be costly to replace
>>>> fixtures. I think he would consider replacing the 12 volt refrigerator if
>>>> he has an inverter.
>>>>
>>>> He definitely wants LiPo batteries.
>>>>
>>>> I don't like the idea of 12 volt direct from a battery plus connecting
>>>> an inverter to that same battery. It is going to be hard to measure and
>>>> monitor things.
>>>>
>>>> I am thinking about using a 48 volt battery with a single phase 120
>>>> volt inverter, getting him to change to a 120 volt refrigerator, and using
>>>> a DC converter to give him somewhere in the range of 100 amps at 12 volts
>>>> for his existing DC lighting and fan loads. Is this a bad idea? Should I
>>>> stick with a 12 volt battery system? He does have a tiny 12 volt pressure
>>>> pump which might be an issue for the converter. I'm not sure. I am a bit
>>>> worried about the efficiency loss and capacity of DC converters and not
>>>> sure how to size it.
>>>>
>>>> Jason Szumlanski
>>>> Florida Solar Design Group
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240424/1e36c91d/attachment.htm>


More information about the RE-Wrenches mailing list